Rookie question: analog outputs at least for TM172 series are either 0-10VCC , 4-20 ma , PWM or ON-OFF. So why is the type INT ? And what happens if output is set to i.e. -5.3 VCC ?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-29 02:21 AM
Hello,
I've checked, with M172P, it's better to limit values to positive ones.
A negative value it's like to write 1000.
A positive value, bigger than 1000, it's limited by bios to 1000.
TM173O instead performs an internal limitation between 0 and 1000
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-29 02:21 AM
Hello,
I've checked, with M172P, it's better to limit values to positive ones.
A negative value it's like to write 1000.
A positive value, bigger than 1000, it's limited by bios to 1000.
TM173O instead performs an internal limitation between 0 and 1000
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-30 04:02 AM
Thanks Federico !
Link copied. Please paste this link to share this article on your social media post.
You’ve reached the end of your document
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.