Posted: 2025-05-29 06:14 AM
A bit like this is not available, but you can easily create it.
You can set a global variable in the boot task and reset it manually, whenever you will find it at true it means the controller rebooted.
You can also store something in the EEprom at boot, in this way you will save the last start.
If you define a DWORD mapped on MD102.0, this is a variable retained by the lithium battery. It can be written continously. Writing on it Date and Time continously, in the boot task you can read it and save into EEprom when the controller has been switched off.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2025-05-29 06:14 AM
A bit like this is not available, but you can easily create it.
You can set a global variable in the boot task and reset it manually, whenever you will find it at true it means the controller rebooted.
You can also store something in the EEprom at boot, in this way you will save the last start.
If you define a DWORD mapped on MD102.0, this is a variable retained by the lithium battery. It can be written continously. Writing on it Date and Time continously, in the boot task you can read it and save into EEprom when the controller has been switched off.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of