Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation
Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively. Register now to secure your spot!

Link object config items to IO/Registers

Geo SCADA and Remote Operations Devices Ideas

Use this portal to submit your innovative ideas to make Geo SCADA Expert and Devices such as SCADAPack, Trio and Realflo of greater value to you and to the SCADA & Telemetry community. Every idea will be individually reviewed by our team for merit and will be marked Under Consideration.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Remote Operations
  • Geo SCADA and Remote Operations Devices Ideas
  • Link object config items to IO/Registers
Options
  • Mark as New
  • Mark as Read
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Labels
Top Labels
  • Alphabetical
  • SCADA 2
  • ViewX 2
  • Mimics 2
  • SCADAPack 2
  • Scripting 1
  • Virtual ViewX 1
  • Geo SCADA Expert 1
  • Efficiency 1
  • Configuration management 1
  • Modbus to WiStar 1
Idea Statuses
  • Submitted 12
  • Under consideration 126
  • Accepted 1
  • Declined 4
  • Partially delivered 0
  • Delivered 0
  • Abandoned 0
Related Products
Thumbnail of EcoStruxure™ Geo SCADA Expert
Schneider Electric
EcoStruxure™ Geo SCADA Expert
114
Thumbnail of SCADAPack 57x
Schneider Electric
SCADAPack 57x
2
Thumbnail of Accutech
Schneider Electric
Accutech
1
Load more
Completed Ideas
  • Accutech Modbus Master gateway to read Modbus devices and incorporate into WiStar net

  • Controller Key Enhancement

  • Restore "Embed Source Code for Upload" Option in Workbench (SP300 family)

  • DNP Outstation And DNP Master Diagnostics

View All
Top Liked Authors
User Likes Count
gabarit
Ensign gabarit
1
Hardin4019
Lieutenant Hardin4019
1
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
4 Likes

Link object config items to IO/Registers

Status: Under consideration Submitted by Lieutenant JG MikeForshock on ‎2020-09-18 11:35 AM
3 Comments (3 New)

Many systems (should) link the appropriate Alarm Points (Low, Low-Low, High, High-High, etc.) operators configure within the HMI/SCADA software (Geo SCADA) to the registers within the controller (PLC).

 

Example:

We have a point with a value between 0-100

High-High: 95

High: 90

Low: 10

Low-Low: 5

These limits would then be linked, bi-directionally, to the appropriate registers in the controller. Modbus in this example.

Point.HighLmtStd <> Controller.400100

 

In the interim we have created a logic script to move the Geo SCADA config values to the created analog output points. This is a single direction and works for "simple" systems, but others with local HMI that allows for these and even some dynamic set point algorithms (avg. deviations...) are not connectable in these manner.

The unfortunate reality is that this significantly increases the Point usage. Perhaps give us a "freebie" that can link within the Advanced drivers point config. That would definitely be appreciated!

Tags (1)
  • Find more ideas tagged with:
  • english
Comment

Link copied. Please paste this link to share this article on your social media post.

  • Back to Idea Exchange
  • Previous
  • Next
3 Comments
sbeadle
Kirk sbeadle Kirk
Kirk
‎2020-12-21 07:24 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2020-12-21 07:24 AM
Status changed to: Under consideration

Thank you Mike.

A similar feature was part of the simple OPC driver but I don't think many people used it.

 

MikeForshock
Lieutenant JG MikeForshock
Lieutenant JG
‎2021-02-18 02:44 PM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-02-18 02:44 PM

@sbeadle 
Missed this update, thanks. 
It would not need be recorded or any other use outside the config of the point.  Hope it gets considered still

du5tin
Lt. Commander du5tin
Lt. Commander
‎2021-03-02 11:16 AM
  • Mark as Read
  • Mark as New
  • Bookmark
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content
‎2021-03-02 11:16 AM

+1 for this request. We maintain and build systems that 'waste' thousands of points on static configuration information because the alarming setpoints live in the RTU/PLC and not in SCADA. It would be awesome to see some of that become bi-directional to reduce integration effort (fewer hours spent configuring ranges and set points on points) and also to make Geo SCADA values more closely match the values in the PLC. 

 

We had looked into the Simple OPC driver functionality a long time ago but we couldn't figure it out. Could also be because our PLC tags didn't match the format it was expecting. 

 

Anyway, this mindset or way of working is very very common in oil and gas on just about every PLC platform. The HMI is just a view of what is in the PLC. 

Comment
Preview Exit Preview

never-displayed

Hint:
@ links to members, content
 
  • Back to Idea Exchange
  • Previous
  • Next
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of