What To Do If DBServer Freezes Indefinitely

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • What To Do If DBServer Freezes Indefinitely
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 07:14 PM
0 Likes
0
1250
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 07:14 PM

What To Do If DBServer Freezes Indefinitely

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 04:14 AM

📖 Home  Back  

 

It is possible, although very rare, that the DBServer process becomes frozen and does not respond to any client (ViewX shows offline for that server, server icon on the desktop is grey and any other servers cannot connect successfully to it). In these scenarios it is likely that a database lock has not been released correctly by a database thread and so that when another database threads requires a databack lock they must wait, and wait, and wait

ClearSCADA 2015 R2 (v77) contains deadlock detection of a Main server from the other hot-standby servers, as part of the polling between servers. In v78 a watch dog mechanism which allows detection and automated restarting of the affected server will be available.

Usually you need to kill the DBServer.exe process using Task Manager and manually start the service for the server to return to operation. Killing the DBServer.exe process is a severe action which will lose any configuration changes or value data not yet flushed to disk or to the Standby servers. It is also possible that the database became deadlocked midway through saving the database to disk, in which case the database may also be considered corrupt at startup.

Only 'you' know your system and how it behaves under typical usage; before killing a server which is/was Main it is worth discussing what was happening on the system that could have caused the problem. Standby servers will resync from the Main server, assuming it is operating correctly, when restarted so the risk in this case is a lot less. Although, in this scenario, the urgency to recover the Standby server is also usually lower.

However, before you kill the process there are some steps to take to ensure that enough information is gathered to ensure that technical support are better able to diagnose the problem and provide resolution.

Gather Database Log Files

As documented in Problem Reporting - Getting the Right Information you need to collect the database log files and snapshot files from the server that is experiencing issues, ideally at least an hour before the server froze to at least five minutes into the freeze. However, if more information either side is available more information may be better.

Additional logging, although this cannot be enabled if ClearSCADA is currently deadlocked:

  • 'Read/Write Lock Diagnostics' is a ServerStatus and DBSnapshot logging feature which should be enabled (via ServerStatus | Database | Read/Write Lock Diagnostics' and right-click column headings in the main pane) which is a modest logging overhead and provides summary information about database lock usage.

 

  • Lock (LCK) database class logging having been enabled before the freeze starts is extremely useful however is not enabled by default and when enabled will generate a lot more logging reducing the coverage of the log files. If this problem keeps occuring then on subsequent restarts ensure this LCK logging is enabled via the ServerStatus program, and if possible the number of DB log files are increased to ensure coverage is sufficient.


If the server is in a Standby state, also collect the log files from the Main server for the same time period where it is possible to ensure that any information from the Main that could have cause the Standby server to freeze is caught for analysis.

Generate a DBServer Minidump

To allow for a better understanding of what the DBServer process was doing at the time of the deadlock a minidump needs to be generated for analysis. The follow section discusses three options, ranging from simple (Task Manager) through to advanced (DebugDiag).

The size of the dump will depend on the tool used and will typically be the size of the virtual bytes of DBServer.exe, depending on the options selected.

Using Task Manager

Producing a dump (MDMP or DMP) file can be achieved via the Windows Task Manager or, often more conveniently and successfully, via an external diagnostic tool created for the purpose. Windows Task Manager on a 64-bit Windows operating system will have two versions, a 32-bit and 64-bit version, and the correct one must be used for target process being dumped.

Using ProcDump

Procdump.exe is a command line application from SysInternals (http://technet.microsoft.com/en-us/sysinternals/default) that will dump a process' current details to a .mdmp file. This file can then be provided to technical support to aid in the analysis of the log files. You will also need psexec.exe, also from SysInternals, to be able to generate a minidump file for DBServer.exe.

The following process assumes you are comfortable and understand the usage of the Windows Command Prompt.

Using this process on a healthy process will cause it to lock up whilst the minidump is generated, which may take a few minutes. Do so at your own risk


1. Copy procdump.exe and psexec.exe to a suitable location on your server. Ensure sufficient disk space exists to store a file size the size of the current virtual memory usage of DBServer. Also install a suitable file compression tool if needed.


2. Open up a Command Prompt. If you're running Windows Server 2008 R2 or Windows Server 2012 R2 then run it as administrator by right-clicking the choosing the 'Run as Administrator' option.


3. Change directories to the location that you copied the procdump and psexec executables to.


4. Using psexec run a Command Prompt as the 'SYSTEM' user. This can be done with the following command:
psexec -s cmd


5. If successful, you will likely be changed to the %WINDIR%\System32 folder. Change back to the directory with the SysInternal executables.


6. Run the following command:

 

 procdump -accepteula dbserver.exe normal.mdmp 

 

This should quickly generate a small minidump file of a few MB in size. The -accepteula switch will automatically accept the dialogue that would normally be shown to a user to accept before the process is ran however as you're running as the SYSTEM account there is nowhere to show the dialogue and instead the process will appear to hang. Refer to the Microsoft website for the EULA for this software, or temporarily run the procdump.exe process as your user to get the dialogue shown.


7. Run the following command:

 

procdump -accepteula -ma dbserver.exe full.mdmp


This will generate a much larger minidump file, basically the entire memory of DBServer.exe and depending on how much memory DBServer.exe is using may take a long time.


8. Provide the normal.mdmp file, along with the log files, to technical support for analysis.


9. Recover the server to operational usage.


10. Compress the full.mdmp (it can be compressed down to about 5% of size using certain compression methods) and store it in a safe place should it be required for analysis.

Note that some company security policies may require the full minidump files be stored in a secure location similar to ClearSCADA database backups as the data contained within that minidump may contain sensitive information such as IP addresses and user names should someone want to data mine the contents*

Using DebugDiag

DebugDiag will provide similar functionality to the above tools, as well as including more information within the minidump file allowing a more detailed analysis.

The tool can be attached to a problematic DBServer process and extra information collected and added to DMP file(s) once installed and can be downloaded from: Debug Diagnostic Tool v2 Update 2 (https://www.microsoft.com/en-us/download/details.aspx?id=49924)

Performance and Memory Problems - Using DebugDiag to track Memory Usage

Preparation

In addition to permission to install the DebugDiag tool, consideration needs to be given to the storage of report files and the very large DMP files output. A DMP file will consist of the Virtual Memory (whole footprint of the process) and the extra information collected, likely to be many GB in size. How will these large DMP files be transferred?

Configuration / Execution

This description covers the approach of creating a rule for the DBServer process, so that the folder location of the reports and dump files can be configured. Using the simple approach of initiating memory analysis from the process list could result in a default location being used and that disk/partition being overrun with DMP file content and affecting the whole host's performance.

Open the collection tool from the Windows, Start, All Programs:

worddav9e4932c606cf29d97511ba627e3831b3.pngworddav9e4932c606cf29d97511ba627e3831b3.pngworddav9e4932c606cf29d97511ba627e3831b3.png

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.