This article details ports used by Geo SCADA and should form the basis for configuration of system firewalls. For client-server connections, you need to create the firewall rules as described here.
The following table includes details about the protocols and ports used by the other Geo SCADA components, such as drivers. You may need to create firewall rules for those components and features (if any) that your system is using.
The information is categorized under these headings:
Protocol | Port(s) | Incoming Connection | Outgoing Connection | Description |
---|---|---|---|---|
TCP or UDP | - | Devices | Drivers | The protocol and ports used by TCP/IP channels for the connections between the devices and the drivers. You can configure the protocol and port by adjusting the Port and TCP/IP Type settings on the Connection tab of the Channel Form in ViewX. |
TCP or UDP | - | Outstations | Drivers | The protocol and ports used by network outstations (outstations that have Ethernet ports that are connected to a network). You can configure the port by adjusting the Port setting(s) on the Network tab of the Outstation Form in ViewX. The protocol for the port(s) is defined by the outstation's network channel (see below). |
TCP or UDP | - | Drivers | Outstations | The protocol and ports used by network channels (channels that are used to connect to network outstations - see above). You can configure the protocol and port by adjusting the Listen Port\Port and TCP/IP Type settings on the Connection tab of the Channel Form in ViewX. |
TCP | 502 | Outstations | Modbus Driver | The port is used by Modbus TCP outstations. You can configure the port by adjusting the Port setting on the Primary Port and Secondary Port tabs of the Scanner Form in ViewX. |
TCP | 502 | Modbus Slave Driver | Modbus TCP Masters | The port is used by Modbus TCP slave outstations. This port is fixed and cannot be re-configured. |
ICMP | Any Network Device | ICMP Driver | Used to test the connection between the main server and any network device. A ping is used to test the connection. You can configure the device by adjusting the Device setting on the Digital Point tab of the Point Form in ViewX. The ICMP protocol does not have ports. |
|
TCP | 102 | Siemens PLCs | Simatic S7 Driver | The port is used by Siemens Simatic S7 network scanners. You can configure the port by adjusting the Port settings on the Primary Connection and Secondary Connection tabs on the Scanner Form in ViewX. |
TCP | - | OPC XML-DA Servers | OPC XML-DA Driver | The port is used by OPC XML-DA servers. You can configure the port by adjusting the OPC Server URL setting on the Server tab of the Server Form in ViewX. The URL includes the server and port of the OPC server, for example, http://opcsvr:8080/xmlda/ for a ClearSCADA server called 'opcsvr' on port 8080. |
UDP | 123 | NTP Servers | NTP Driver | The port is being used by the Network Time Protocol servers. You can configure the NTP server by adjusting the NTP Server setting on the Scanner tab of the Scanner Form in ViewX. The protocol and port are fixed and cannot be re-configured. |
TCP | 20876 | Port Server | Drivers | The ports used for remote serial channels (dynamic ports). This is fixed and cannot be re-configured. Each serial port will use a different TCP/IP port number. |
TCP | - | Port Server | Drivers and Third Party | The port for remote serial channels (static ports). You can configure the static ports by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\PortServer/Ports registry key. The name of each value in the key is a port number. For more information, see the Port Server documentation in the Server Administration Guide in ClearSCADA Help. |
TCP | 0 | Server | Telnet Clients | The ports used by the Telnet server for server monitoring. Each Telnet server will use a different port. The port that is currently being used is shown in the General\Information\Telnet Server section of the Server Status Tool. You can configure the port by using the System Configuration\Logging\Server\Telnet Port setting on the Server Configuration Tool. For more information, see the Server Administration Guide in ClearSCADA Help. |
TCP | 0 | Drivers | Telnet Clients | The ports used by the Telnet server for driver monitoring. Each Telnet server will use a different port. The port that is currently being used is shown in the Telnet Port column in the General/Modules section of the Server Status Tool. You can configure the port by right-clicking on the individual driver in the General/Modules section of the Server Status Tool and then choosing the Logging option. This displays the Logging Configuration window. On the Configuration tab, you can change the port that is used by the driver by entering the required port number in the Telnet Port field. |
TCP | 0 | Drivers (Channels) | Telnet Clients | The port is used by the Telnet server for driver channel communications logging. The port that is currently being used in shown in the View window for the relevant channels. You can configure the port by using the Enable Telnet pick action and entering the required port at the prompt. You can also define the port as a parameter for the EnableTelnet method. |
TCP | 0 | Port Server | Telnet Clients | The port is used by the Telnet server for port server logging. The port that is currently being used is shown in the header of log files. You can configure the port by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\PortServer\LogTelnetPort registry key. For more information, see the Port Server documentation in the Server Administration Guide in ClearSCADA Help. |
TCP | 0 | License Server | Telnet Clients | The port is used by the Telnet server for license server logging. The port that is currently being used is logged in the header of log files. You can configure the port by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\LicenceServer\LogTelnetPort registry key. |
TCP | 0 | Alarm and Event Printer | Telnet Clients | The port is used by the Telnet server for OPC alarm and event printer logging. The port that is currently being used is shown in the header of log files. You can configure the port by editing the HKEY_LOCAL_MACHINE\SOFTWARE\Serck Controls\SCX6\AEPrinter\LogTelnetPort registry key. |