Connect to ClearSCADA Using OPC - OPC Protocol Details

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Connect to ClearSCADA Using OPC - OPC Protocol Details
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Application Programming 12
  • Setup 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Support 5
  • IoT 5
  • SCADA 5
  • Geo SCADA Expert 5
  • Drivers and Communications 4
  • Security 4
  • DNP 3 3
  • IEC 61131-3 Logic 3
  • Trends and Historian 2
  • Virtual ViewX 2
  • Geo Scada 1
  • ClearSCADA 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Architectures 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • OPC UA - Driver and Server
  • Requirements for Generating a Valid OPC UA Server Certificate
  • Load Events Using LoadRecord and LoadRecords
  • Geo SCADA Embedded Component Licenses
  • Geo SCADA 2023 Known Issues
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 02:57 PM
1 Like
0
1740
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 02:57 PM

Connect to ClearSCADA Using OPC - OPC Protocol Details

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 11:57 PM

📖 Home  Back  
OPC is based on Microsoft DCOM, and the terms In Process Server, Local Server, and Remote Server are all options when a client connects to a server. These options are available in the OPC Server database object. More specifically they are the flags arguments passed to the CoCreateInstanceEx call under WIN32.
  • In Process means that the server is a Dynamic Link Library located on the local machine. This is the only option that can be used to connect to an ClearSCADA server because ClearSCADA OPC Servers are provided as an In-Process DLL.

  • Local Server means that the server is an executable located on the local machine. This is usually the option used with 3rd party OPC Servers, because most are provided as an EXE.

  • Remote Server means that the server is an executable located on another machine. To successfully launch or connect to a remote server, user account details have to be entered to specify which user account should be used in accessing the remote machine.


You can only specify DCOM security for Remote Server activations, for In Process and Local Server activations security credentials passed to the CoCreateInstanceEx call are ignored.

To provide additional security, the OPC foundation defines a private security interface. If you select the option "Use Private Security", the OPC client driver will attempt to log on to the OPC Server using the private security interface. The ClearSCADA OPC server supports this interface and maps private security log on requests directly onto ClearSCADA user accounts. So for a system using ClearSCADA to monitor server statuses, ensure that either the everyone user has read access to the database, or private security is enabled on the OPC server definition that uses an ClearSCADA user who has read privilege.

OPC Servers should support a registration mechanism to put the appropriate entries in the registry. ClearSCADA registration is done through the ClearSCADA Client Connections control panel applet (also available in the Start Menu). In process servers are registered using RegSvr32. Executable servers are registered through the /RegServer command line option. Registration of remote servers is more difficult, in that the server has to be registered on the server and client machines.

In terms of OPC server browsing, ClearSCADA uses the category manager to browse for OPC servers. This technique was introduced by the OPC foundation some time during the OPC DA 2 specification. The previous technique was for an OPC server to include an extra OPC key under the CLSID to indicate that this is an OPC server. New servers are supposed to register themselves using both mechanisms, i.e. using the category manager and using the OPC key under the CLSID. Some very old servers only use the OPC key technique and will not be visible to ClearSCADA. If you run OLEView (an OPC Tool) in "Expert" mode you should see OPC categories in the "Grouped By Component Category" section.

Go: Home Back
  • Tags:
  • SCADA Innovation

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now