ClearSCADA 2015 R1 Known Issues

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2015 R1 Known Issues
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 05:09 PM
0 Likes
0
971
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 05:09 PM

ClearSCADA 2015 R1 Known Issues

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 02:09 AM

📖 Home  Back  
Please read the information below prior to installing SCADA Expert ClearSCADA 2015 R1 for important information on any known issues.

Issue when using Windows 10 Creators Update - build 1703 (issue reference: SUP-9419)



A problem has been identified within WebX clients after upgrading to the Windows 10 Creators update build 1703 whereby the scroll bars on an embedded list control (e.g. SQL Query, Event List, Alarm List on a mimic) in WebX no longer work as expected. We are actively working with Microsoft on this problem, which has been recently confirmed as an issue in MS Internet Explorer. MS Issue Reference: REG 117052415792436.

Current advice for ClearSCADA customers using WebX is that they should avoid upgrade of their Windows 10 clients to Creators Update build 1703 until this issue is resolved.

_Customers impacted by the above are encouraged to raise this directly to Microsoft via their Support Channels, quoting the Issue Reference: REG 117072016066603, to help facilitate a timely resolution._

Recent testing has uncovered a potential work-around; when using Google Chrome browser and the IE Tab Extension (which simulates an Internet Explorer browser) version 10.7.31.1 we were able to successfully use the embedded mimic's scrollbars. The following considerations apply:
  • We have not formally tested WebX using Google Chrome's IE Tab Extension.

  • Using Chrome web browser may be a problem for some customers (e.g. a Security Policy might exclude the use of Google Chrome browser, or the extension kits)

  • The extension may be using an older version of Windows library, and a newer version of the extension might reveal the problem again.


Thanks for your support, but overall we apologize for any inconvenience.

ViewX User Interface



"All Window" Favourites (issue reference: SUP-8510 and SUP-8246)


The following issues have been identified regarding All Window Favourites (aka Super Favourites), whereby the windows are not restored as saved. Specifically:

  • The Tab Order is not preserved when saving/restoring the favourites, but instead a default Tab Order is used.

  • The Screen Layout is not preserved when saving/restoring the favourites, such that any personalisation of the screen layout to provide horizontal- or vertical-tiling is not remembered and all windows are restored within a single tab group.

  • When using multiple Window Containers within a multi-monitor configuration, all windows within a Secondary Window Container are not restored to the Secondary Container, but instead are restored to the Primary Container alongside any existing Primary Window Container windows.

  • Inset Windows are not restored, but instead only the Main Window is restored.



Performance of Locate... Operations


Databases that have an excessive number of objects, or objects within a flat database hierarchy, may experience delays when attempting to execute one of the following:
  • Locate in Database Explorer

  • Locate in OPC Explorer

  • Locate Template

  • Locate in Template


These delays may cause ViewX to display a 'busy' icon while this action is performed, but should remain responsive for further user input. Once the executed action is complete, the respective Database or OPC Explorer will display the target object.

Command Line Parameters


The command line parameter "/head:" has been removed from ViewX after ClearSCADA 2013 R2. This has been replaced by "/instance:" for multiple instances, and with "/startup:" for enhanced multi-monitor functionality, where is the location of a startup configuration file. Guidance on migrating between the old ViewX command line parameters and the new multi-monitor options is available in the ViewX Upgrade Notes. 

More information on the improved multi-monitor support can be found within the ClearSCADA 2015 R1 online help guide under: Core Reference > Client Administration > Client Administration Guide - Launch a ViewX Client on a Multi-Monitor Setup.

Maximum Windows Limitation


ViewX now enforces a maximum limit of 100 open windows. Any system previously configured for 0 (and hence unlimited) windows will now be set to 100. Attempts to exceed the configured limit will result in normal Maximum Window behaviour requesting a user to close an existing window to proceed.

Time Format Symbols


The following time format symbols are no longer supported in ViewX (from ClearSCADA 2014 R1 onwards) due to their inconsistency with the .NET Time Format. This does not impact the operation of the ClearSCADA Server or the validity of any time/date formatting, but any use of the following time format symbols should be removed to ensure correct display of date/time to the user:
  Symbol   Meaning   Presentation   Example
  e   day of week (1~7)   (Number)   2
  D   day of year   (Number)   189
  F   day of week in month   (Number)   2
  w   week in year   (Number)   27
  W   week in month   (Number)   2
  k   hour in day (1~24)   (Number)   24
  K   hour in am/pm (0~11)   (Number)   0


User Specific Settings


When upgrading from previous versions of ClearSCADA (prior to ClearSCADA 2014 R1) any user-specific ViewX display settings will be lost. This includes, but is not limited to; layout of Toolbars, width/visibility of the Database and other Explorers, and the position of the Alarm Banner.

Alarms Not Available


After upgrading to ClearSCADA 2015 R1 alarms might not be shown in any client, such as the ViewX alarm banner, or any alarm functions being shown on menus. In ClearSCADA 2015 R1 alarms can be enabled or disabled in the server's configuration and on upgrade some servers are not defaulting correctly to having alarms enabled. To enable alarms, use the Server Config tool and enable alarms as shown in the following image.

AlmEvtEnable.pngAlmEvtEnable.pngAlmEvtEnable.png

You will need to manually restart any client application connected to that ClearSCADA server for the changes to take effect, or restart the server to force all clients to reconnect.

This setting can be set manually via the Registry prior to starting the ClearSCADA service using the value 'HKEY_LOCAL_MACHINE\SOFTWARE\Schneider Electric\ClearSCADA\DB\AlarmsEventEnabled' and setting the REG_SZ value to 'True'. If this Registry setting is changed after the ClearSCADA service is started, the service must be restarted for the changes to take effect.

WebX User Interface



Annotation not translated in trend


Translated strings for a user with the user set to the locale for those translations, a trend created and an internal digital point's processed history trace added to it. Annotations are then added to the trend with the translation string: @this. ViewX and old WebX displayed the translation for @this correctly, but new WebX displays @this instead of the translation for @this.

Crystal Reports



A problem with exporting Crystal Reports on Windows 8 and 8.1, and Windows Server 2012 and 2012 R2 has been identified. It is triggered by the report containing Boolean parameters with the "Exclusive group" option enabled. Subject to confirmation the likely cause is the SAP crystal runtime rather than ClearSCADA 2015 R1.

Installer



OPC Registration


On a clean installation of SCADA Expert ClearSCADA 2015 R1, the classes for OPCDA, OPCAE and OPCHDA are not registered. The user would need to open the Client Configuration dialog and click OK on the configured connection for the classes to be registered. This was changed to add support for the Systems.xml file.

Installation of Microsoft Redistributables


Installation of Microsoft Redistributable packages have been found to intermittently terminate prematurely when running on a PC with limited available system resources, which causes the ClearSCADA installation to be aborted. Running the ClearSCADA installation again has shown good success in resolving these intermittent installation problems, although may have to be repeated a number of times if the errors persist.

Support for Internet Explorer 9/10/11



The following problems were identified:
  • When clicking on the 'List All Objects' from a class information page in the database schema, the list of objects may not display correctly. This is a problem with the Internet Explorer's XSL transformation related to elements with content and children.

  • Script functions such as 'Mimic.OpenInset' and 'App.OpenWindow' may not display properly on IE9/10/11.

  • Hyperlinks to lists may not display correctly due to the cross site scripting security filter in Internet Explorer. This also includes links to trends generated using the TrendSpec specification in ClearSCADA. The workaround for this is to disable the Cross-Site Scripting (XSS) filter in the web browser.


Go: Home Back
  • Tags:
  • SCADA Innovation

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore