Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Share Your Feedback – Help Us Improve Search on Community!
Please take a few minutes to participate in our Search Feedback Survey. Your insights will help us deliver the results you need faster and more accurately.
Click here to take the survey

ClearSCADA 2015 R1.1 Upgrade Strategy

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • ClearSCADA 2015 R1.1 Upgrade Strategy
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Virtual ViewX 2
  • Trends and Historian 2
  • Architectures 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Geo Scada 1
  • Tools & Resources 1
  • Privacy Policy 1
  • OPC-UA 1
  • ClearSCADA 1
  • Python 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Python API - Reading the Instance and Template Structure
  • Python API - How to get Earthquake data into a Geo SCADA Map
  • Python API - Creating and Configuring Data Tables
  • Python API - Setting aggregates
  • Python API - Clearing an aggregate link
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 06:15 PM
0 Likes
0
765
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 06:15 PM

ClearSCADA 2015 R1.1 Upgrade Strategy

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 10, 2021 03:15 AM

📖 Home  Back  
This document outlines the recommended strategies for upgrading to SCADA Expert ClearSCADA 2015 R1.1.

For details on version compatibility of clients and servers as well as server-server for redundancy, please refer to the ClearSCADA Version Compatibility Matrix.

Important Information



Updating your ClearSCADA License



Prior to performing an upgrade of your ClearSCADA software, it is necessary to evaluate whether your current license is compatible with the new version of ClearSCADA.

License keys may need to be updated when upgrading to a new major or minor release. Provided that the server license you have supports a server version greater than, or equal to, the version of ClearSCADA to which you are upgrading, you do not need to update your license. If the ClearSCADA software version is greater than the license version, you will need to upgrade your existing license.

To determine your ClearSCADA version, please refer to the steps within Determine Your ClearSCADA or Geo SCADA Version.

To determine the version of your ClearSCADA server license, or to update your existing license, refer to the steps within Updating Your ClearSCADA License.

Changes to Upgrade Strategy



As a result of the changes to the ViewX User Interface for ClearSCADA from 2014 R1 onwards, the strategy for upgrading to ClearSCADA 2015 R1.1 from versions prior to 2014 R1 has been modified. Adhering to the previous strategy of upgrading ViewX clients prior to the ClearSCADA server will result in these upgraded clients being unable to communicate with the system until the server is also upgraded to ClearSCADA 2015 R1.1.

The recommended strategy for upgrading to ClearSCADA 2015 R1.1 is to upgrade the ClearSCADA server(s) first, followed by any remote clients. Previous versions of ViewX will provide remote clients with continued connectivity with ClearSCADA before and after the upgrade to ClearSCADA 2015 R1.1, after which time these clients can be upgraded to ClearSCADA 2015 R1.1.
It is recommended that all ViewX clients be upgraded to ClearSCADA 2015 R1.1 following successful upgrade of the server(s).


Server emulation is not required to support previous ViewX clients and should not be enabled on a ClearSCADA 2015 R1.1 Server.



Supported client versions include ClearSCADA 2013 R2, ClearSCADA 2014 R1 and ClearSCADA 2015 R1 (and corresponding Service Packs for each version).
ViewX clients prior to ClearSCADA 2010 R3 will not be able to connect to a ClearSCADA 2015 R1.1 server.



Removal of the Integrated PLC Driver



ClearSCADA software versions prior to 2014 R1 had an option of an integrated Kepware Technologies KEPServerEX4 PLC driver; however with the evolution of ClearSCADA this integrated PLC driver suite previously is no longer available.

To ensure the continuous, long-term operation of your system we recommend that you migrate to an external installation of KepServerEX5 (Kepware's latest version) prior to the upgrade to ClearSCADA 2015 R1.1. This migration will require the conversion of any existing PLC database objects into corresponding OPC database objects, for which a documented procedure and software tool has been prepared and will be provided free of charge from Schneider Electric on request.

An upgrade to ClearSCADA 2015 R1.1 should be performed only after all PLC database objects have been migrated to corresponding OPC database objects.

Upgrading from ClearSCADA 2015 R1



With a Standalone Server



  • Shut the server down.

 

  • Upgrade the server to SCADA Expert ClearSCADA 2015 R1.1.

 

  • Restart the server.



With both Main and Standby Servers



  • Shut down the Standby server.

 

  • Upgrade the standby server to SCADA Expert ClearSCADA 2015 R1.1.

 

  • Restart the standby server.

 

  • Wait for the server to fully synchronize with the main server and go into the standby state.

 

  • Connect a ViewX client to the upgraded standby server and confirm the client can connect and operate the system.

 

  • Switch the upgraded standby server over to become main.

 

  • Connect a ViewX client to the upgraded standby server (which is now main) and confirm the client can connect and operate the system.

 

  • If there are any problems identified, reinstate the previous main server (which is now running as standby) and contact ClearSCADA Technical Support.

 

  • Repeat upgrade for additional standby server(s).

 

  • Upgrade the previous main server to SCADA Expert ClearSCADA 2015 R1.1.

 

  • Restart the previous main server. The server will synchronize with the new main server and go into the standby state.




On a system with numerous clients connected to the servers, it is recommended that the servers be upgraded before the clients to ensure a smooth upgrade path.




To take advantage of the numerous improvements in this version, it is strongly recommended that both the servers and clients be upgraded to SCADA Expert ClearSCADA 2015 R1.1.



Other Versions



To upgrade from versions older than ClearSCADA 2015 R1, please follow the instructions shown in the Upgrade Strategy for ClearSCADA 2015 R1 (using 2015 R1.1 instead of 2015 R1).


ViewX clients prior to ClearSCADA 2010 R3 will not be able to connect to a ClearSCADA 2015 R1.1 server.



Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore