Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Calculating the Server Point Count

Geo SCADA Knowledge Base

Access vast amounts of technical know-how and pro tips from our community of Geo SCADA experts.

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • Knowledge Center
  • Geo SCADA Knowledge Base
  • Calculating the Server Point Count
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Labels
Top Labels
  • Alphabetical
  • database 32
  • Web Server and Client 31
  • WebX 19
  • Request Form 18
  • Lists, Events & Alarms 16
  • ViewX 15
  • Setup 12
  • Application Programming 12
  • Telemetry 8
  • Events & Alarms 7
  • Lists 7
  • Mimic Graphics 7
  • Downloads 6
  • Geo SCADA Expert 5
  • SCADA 5
  • IoT 5
  • Support 5
  • Drivers and Communications 4
  • Security 4
  • 2025 3
  • IEC 61131-3 Logic 3
  • DNP 3 3
  • Trends and Historian 2
  • Virtual ViewX 2
  • Architectures 1
  • Geo Scada 1
  • Templates and Instances 1
  • Releases 1
  • Maps and GIS 1
  • Mobile 1
  • Tools & Resources 1
  • ClearSCADA 1
  • Privacy Policy 1
  • OPC-UA 1
  • Previous
  • 1 of 4
  • Next
Latest Blog Posts
  • Sparkplug Quality Mapping
  • Geo SCADA 2025 Upgrade Strategy
  • Geo SCADA 2025 Known Issues
  • Geo SCADA 2025 Upgrade Notes
  • Geo SCADA 2025 Operating System Support
Related Products
product field
Schneider Electric
EcoStruxure™ Geo SCADA Expert

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Anonymous user
Not applicable
‎2021-06-09 02:58 PM
0 Likes
0
1288
  • Bookmark
  • Subscribe
  • Email to a Friend
  • Printer Friendly Page
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2021-06-09 02:58 PM

Calculating the Server Point Count

Originally published on Geo SCADA Knowledge Base by Anonymous user | June 09, 2021 11:58 PM

📖 Home  Back  

 

The licensed point count is made up of the sum of the number of point objects and pulse objects.
There are at least three ways to determine the point count currently being used by a server.

 

Server Status Dialog

The first approach (and simplest) is to open the server status dialog by right clicking on the server icon and selecting status. At the bottom of the Info tab, the current licence details are shown. This method will list the number of points currently used as well as the total number of points available in the licence.


PointCount.PNGPointCount.PNGPointCount.PNG
Database Queries

The second approach to determining a point count is to use the Queries views available in ViewX. Open the Queries views by selecting the queries icon in the toolbar. From the Queries section, double click on the Points table and select OK on the filter dialog to show all points. When the list is displayed, the number of rows in that list (displayed in the status bar at the bottom of the ViewX window) tells the number of points in the system.


For pulse points, repeat the process using the Pulse Actions table. The sum of the two numbers should give the total points.
This same mechanism can be used to determine point counts in any section of the database.


The actual queries run for points and pulses are as follows:

SELECT COUNT(y) FROM CDBPOINT
SELECT COUNT(y) FROM CDBPULSE
Using the SQL query format will only provide accurate results if the user you are logged in with has permissions to view all database point and pulse objects. Any object where you do not possess appropriate permissions will not be returned and so the apparent point count will be less than its actual value.

 

Logic

You could use a logic program to store the used points in an internal analog point in the database. This method gets around the possibility of all points not being returned in a query due to permissions, since logic runs under a high level account which has access to all points.

TYPE
Result:
STRUCT
Count : DINT;
END_STRUCT;
END_TYPE

PROGRAM LicenceCount
VAR NOCACHE
Points AT %S(SELECT COUNT(*) AS "Count" FROM CDBPOINT) : RESULTSET OF Result;
Pulses AT %S(SELECT COUNT(*) AS "Count" FROM CDBPULSE) : RESULTSET OF Result;
Output AT %M(.Licence Usage.CurrentValue) : DINT;
END_VAR

Output := Points.Value.Count + Pulses.Value.Count;

END_PROGRAM


The output is to an internal analog point. Remember to change the Hand Control range and FullScale property as necessary so the logic doesn't attempt to write out of range values and throw an error.

Go: Home Back

Author

Biography

Anonymous user

Link copied. Please paste this link to share this article on your social media post.

  • Back to Blog
  • Newer Article
  • Older Article
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore