Dear sir/madam,
hello, may i ask what is the max number of zigbee sensor connection can comx510 be support with the Zigbee USB in it?
https://www.se.com/ww/en/product/EBXA-USB-ZIGBEE/zigbee-receiver-for-com%27x-200-210-510/
many thanks.
Best Regards,
Tony Leung
Link copied. Please paste this link to share this article on your social media post.
Hi Tony,
As stated on page 70 of the Com'X 510 Energy Server User manual, the maximum number of Zigbee devices that can be connected to the Com'X 510 is 20.
Randi
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user ,
For Zigbee sensors like PowerTag or CL110/TH110 we are promoting the PowerTag Link to be connected to the Com'X.
This ZB Gateway is supported by the most recent FW of the Com'X. With an A9XMWD100 you will be able to connect 60 wireless devices (Com'X limit) to the Com'X.
Regards,
Romain
Link copied. Please paste this link to share this article on your social media post.
Hi Tony,
As stated on page 70 of the Com'X 510 Energy Server User manual, the maximum number of Zigbee devices that can be connected to the Com'X 510 is 20.
Randi
Posted: 2020-08-25 07:29 PM
Link copied. Please paste this link to share this article on your social media post.
Thanks, i thought it could be more after the firmware upgrade.
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user ,
For Zigbee sensors like PowerTag or CL110/TH110 we are promoting the PowerTag Link to be connected to the Com'X.
This ZB Gateway is supported by the most recent FW of the Com'X. With an A9XMWD100 you will be able to connect 60 wireless devices (Com'X limit) to the Com'X.
Regards,
Romain