Hi,
I hope this question is on the correct group. If not, please help me to find the correct one.
I have a ZBRN32 which I am using as a WAP for TH110 and CL110 sensors. I am using the documentantion from the ZBRN1 and 2 but have found that there are differences between them and the 32 in the modbus mapping. I am connected with ModbusRTU and am able to get responses from the device.
It seems (for example) that the Radio Channel has moved from Register Address 4024 to 4018.
A second problem that I have is the the wirless signal strength is zero (and the led indicates that as well) although the configuration indicates that it is RUNning. I have paired 3 CL110s but the data I read seems to indicate that they are not being read.
a. Can someone help with the ZBRN32 manual.
b. If not, does anybody know what I am doing wrong ?
regards
Charles.
Link copied. Please paste this link to share this article on your social media post.
Hello @CharlesV ,
ZBRN32 is not a gateway supported by this community.
However, check these threads to have some help:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello Romain,
Thank you for the reply.
Do you know where I might find the right group to get some support ?
regards,
Charles.
Link copied. Please paste this link to share this article on your social media post.
Hello,
If you are using the latest FW ZBRN32 should behave similarly as ZBRN1/2. ZBRN1/2 documentation is available on se.com as true SE industry product. For support you have to get in touch with SE.
There is one big difference with Timeout for TH/CL. ZBRN32 will keep the last measurement received and you have to handle the timeout. ZBRN1/2 will provide NaN in case of timeout.
ZBRN32 is mandatory for SMD MV, I am recommending the use of ZBRN1/2 rather than ZBRN32 if you do not have SMD MV.
PAS or PTL support also TH/CL as Zigbee Gateway.
Kind Regards
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.
With achievable small steps, users progress and continually feel satisfaction in task accomplishment.
Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.
of