Panel Server's recommended number of TCP devices

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server's recommended number of TCP devices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Song-hee
Ensign Song-hee Ensign
Ensign

Posted: ‎2023-11-08 06:49 PM . Last Modified: ‎2023-11-08 06:53 PM

0 Likes
3
1870
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-08 06:49 PM

Panel Server's recommended number of TCP devices

Hello,

We are on design and estimation stage for PAS with multiple meters, there is any recommended number of devices to the communicaion performance?

In the user guide tells 64 for max connetion, and the release notes tells 32 devices for the maximum number of Modbus/TCP concurrent connections.

I'd to avoid some trouble issue of communication performance, let me know the general connection number of slave devices with PAS.

Songhee_1-1699498398633.png

 

Songhee_0-1699498371443.png

 

Labels
  • Labels:
  • Legacy Gateways & Energy Servers
  • Product selection
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
MarianTodorov
Ensign MarianTodorov Ensign
Ensign

Posted: ‎2023-11-09 03:47 AM

1 Like
0
1841
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-09 03:47 AM

Hello,

 

My understanding on this topic is that PAS can read up to 64 devices via Modbus TCP. The 32 Modbus TCP concurrent connections are to define the limit of devices/systems which can read through PAS at the same time. For instance PME, EPO, EBO, ION devices reading data from serial devices under PAS.

 

Best regards,

Marian

See Answer In Context

Reply
Replies 3
Grant_IPACS
Commander Grant_IPACS
Commander

Posted: ‎2023-11-08 09:30 PM

1 Like
0
1859
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-08 09:30 PM

64 is because you can  have a 'slave' PAS off a master PAS, both having 32 devices each maximum = 64 devices, voila!

Regards

Grant
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-11-08 09:59 PM

2 Likes
0
1857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-08 09:59 PM

Hello,

you have the modbus client that allows to connect modbus device. Limit is now 128 (1.7) instead of 64. this is the theoritical calculation but I would expect that performance testing has been made depending on the type of modbus tcp devices. I saw a calculator for EEH.

Regarding modbus server, it is a feature that allow you to poll from a modbus client data from the PAS. If you have activated modbus server on ETH1 as an example you can poll whatever device from the PAS using the Virtual id. Having maximum 64 concurrent tcp connection should be enough.

Kind Regards,

Reply
MarianTodorov
Ensign MarianTodorov Ensign
Ensign

Posted: ‎2023-11-09 03:47 AM

1 Like
0
1842
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-09 03:47 AM

Hello,

 

My understanding on this topic is that PAS can read up to 64 devices via Modbus TCP. The 32 Modbus TCP concurrent connections are to define the limit of devices/systems which can read through PAS at the same time. For instance PME, EPO, EBO, ION devices reading data from serial devices under PAS.

 

Best regards,

Marian

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore