Hi,
I hope this question is on the correct group. If not, please help me to find the correct one.
I have a ZBRN32 which I am using as a WAP for TH110 and CL110 sensors. I am using the documentantion from the ZBRN1 and 2 but have found that there are differences between them and the 32 in the modbus mapping. I am connected with ModbusRTU and am able to get responses from the device.
It seems (for example) that the Radio Channel has moved from Register Address 4024 to 4018.
A second problem that I have is the the wirless signal strength is zero (and the led indicates that as well) although the configuration indicates that it is RUNning. I have paired 3 CL110s but the data I read seems to indicate that they are not being read.
a. Can someone help with the ZBRN32 manual.
b. If not, does anybody know what I am doing wrong ?
regards
Charles.
Link copied. Please paste this link to share this article on your social media post.
Hello @CharlesV ,
ZBRN32 is not a gateway supported by this community.
However, check these threads to have some help:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello Romain,
Thank you for the reply.
Do you know where I might find the right group to get some support ?
regards,
Charles.
Link copied. Please paste this link to share this article on your social media post.
Hello,
If you are using the latest FW ZBRN32 should behave similarly as ZBRN1/2. ZBRN1/2 documentation is available on se.com as true SE industry product. For support you have to get in touch with SE.
There is one big difference with Timeout for TH/CL. ZBRN32 will keep the last measurement received and you have to handle the timeout. ZBRN1/2 will provide NaN in case of timeout.
ZBRN32 is mandatory for SMD MV, I am recommending the use of ZBRN1/2 rather than ZBRN32 if you do not have SMD MV.
PAS or PTL support also TH/CL as Zigbee Gateway.
Kind Regards