Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi admin,
I have problem with COMX510.
I havs 2 line Modbus RS485. Now, i connect 2 line to 2 port RS485 of COM'X. 510.
But when I config in web, I see just 1 spot config for RS485. So, I don't COM'X510 can connect and work parallel to 2 port RS485.
Thanks very much
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user ,
Answered to @SESA528 offline.
Bellow : elements of answers provided.
On Com'X devices you have only 1 RS485 port available. Both serial port are internaly connected.RJ45 Modbus port is connected to the RS485 connector.
=> Having 1 serial port settings under the Com'X Web Interface is an expected behavior. Com'X can manage only 1 RS485 communication
=> We do not offer an alternative to EGX200 that have 2 RS485 COM Ports.
Regards.
Posted: 2020-09-28 02:12 AM
Link copied. Please paste this link to share this article on your social media post.
Hi the community members can you help this member, please?
@Romain_Polette do you think you can advise on this topic?
Link copied. Please paste this link to share this article on your social media post.
Hello @Anonymous user ,
Answered to @SESA528 offline.
Bellow : elements of answers provided.
On Com'X devices you have only 1 RS485 port available. Both serial port are internaly connected.RJ45 Modbus port is connected to the RS485 connector.
=> Having 1 serial port settings under the Com'X Web Interface is an expected behavior. Com'X can manage only 1 RS485 communication
=> We do not offer an alternative to EGX200 that have 2 RS485 COM Ports.
Regards.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.