PM5100 METER DIGITAL OUTPUT TO COMX510 TO VIEW kWh consumption

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PM5100 METER DIGITAL OUTPUT TO COMX510 TO VIEW kWh consumption
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
106
Guillaume_Evrard
Commander Guillaume_Evrard Commander
49
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
XtianPilarcA
Lieutenant JG XtianPilarcA
Lieutenant JG

Posted: ‎2020-10-23 01:28 AM

0 Likes
2
954
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-23 01:28 AM

PM5100 METER DIGITAL OUTPUT TO COMX510 TO VIEW kWh consumption

Dear All,

 

Good day. Since the absence of communication option of PM5100, Is it posible to use the digital output of the said meter's model to comx510 for kWh monitoring via COMX510 web server? 

 

Thank you.

Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-10-23 06:06 AM

1 Like
0
947
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-23 06:06 AM

Hi Romain,

 

No, we are not planning on integrating the PM5100 as a Pulse Meter.  I can mention it to the Offer Manager and see if this is something we'd like to add in the future.

 

Best regards,

Randi

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-10-23 02:19 AM

0 Likes
1
949
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-23 02:19 AM

Hi @XtianPilarcA , 

 

You can connect the DO of the PM5100 directly on a Digital Input of the Com'X510. Please refer to the Com'X510 IS for wiring instructions.

 

PM5100 is not natively supported by the current 6.5.5 Com'X510 firmware. You need to create a device based on a Pulse Meter Custom Model. You will need to define what is the Pulse Weight and some other parameters.

 

@Randi_Dolan Do you know if the next Com'X 510 FW will integrate the PM5100 as a Pulse Meter in the library ?


Thanks.

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Randi_Dolan
Commander Randi_Dolan Commander
Commander

Posted: ‎2020-10-23 06:06 AM

1 Like
0
948
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-10-23 06:06 AM

Hi Romain,

 

No, we are not planning on integrating the PM5100 as a Pulse Meter.  I can mention it to the Offer Manager and see if this is something we'd like to add in the future.

 

Best regards,

Randi

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of