Updating PAS Firmware on 3/4G router(slow network) via remote VPN login

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Updating PAS Firmware on 3/4G router(slow network) via remote VPN login
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server Universal

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
wasabi
Lieutenant JG wasabi Lieutenant JG
Lieutenant JG

Posted: ‎2023-12-04 05:13 PM

0 Likes
2
1225
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-04 05:13 PM

Updating PAS Firmware on 3/4G router(slow network) via remote VPN login

Hi team,

I have a question about updating the PAS to the latest firmware via VPN remote access.

We have a few PAS600 deployed with a 3-4G router connected and I can connect to them via OpenVPN and using remote access via SE portal. However, it is slow in uploading the file and times out.. is there another method to upload .sedp file via SFTP directly to the root of the PAS ?

I have also tried using Power Commissioning App however same issue, it timesout.

 

Regards,

 

  • Thumbnail of EcoStruxure Panel Server Universal
    Schneider Electric
    EcoStruxure Panel Server Universal
View products (1)
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: ‎2023-12-05 07:22 PM . Last Modified: ‎2023-12-05 07:25 PM

0 Likes
0
1179
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-05 07:22 PM

Hi Wasabi @wasabi 

As you have already pointed out on slow network it is an obvious reason for the time out. Firmware update requires a stable, reliable & faster connectivity to the device.

As of now, SFTP in PAS is only for publication and not enabled for any file upload like FW upgrade. So its not possible to do Firmware upgrade via SFTP. (likely part of Cybersecurity reason).

 

 

Regards
Udhayakumar A K
ESXP System Support Expert

See Answer In Context

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Reply
Replies 2
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-12-04 09:20 PM

0 Likes
0
1211
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-04 09:20 PM

Hello,

Sometimes using Edge Management Portal (EMP) it can success, but if you have a bad connectivity you might increase your data consumptions with multiple retries.

Kind Regards

Reply
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: ‎2023-12-05 07:22 PM . Last Modified: ‎2023-12-05 07:25 PM

0 Likes
0
1180
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-05 07:22 PM

Hi Wasabi @wasabi 

As you have already pointed out on slow network it is an obvious reason for the time out. Firmware update requires a stable, reliable & faster connectivity to the device.

As of now, SFTP in PAS is only for publication and not enabled for any file upload like FW upgrade. So its not possible to do Firmware upgrade via SFTP. (likely part of Cybersecurity reason).

 

 

Regards
Udhayakumar A K
ESXP System Support Expert
  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore