Connect RS485 to PAS600

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Connect RS485 to PAS600
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2023-11-23 07:04 PM

0 Likes
7
2875
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-23 07:04 PM

Connect RS485 to PAS600

Hi team,

 

My customer concern about ability number device connect to Panel Server via RS485 (PAS600).

How many is the largest number of RS485 device connect to PAS600?

SESA_B_0-1700795030751.png

Thanks very much

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • Commissioning
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: ‎2023-11-24 12:55 AM

1 Like
0
2863
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-24 12:55 AM

Hi @SESA_B 

 

Adding to @Guillaume_Evrard comments, PAS can support up to 32 devices without repeater if the slave devices & RS485 wiring are as per the standard. Please refer this guidance for more information's and follow the wiring recommendations highlighted for better performance. https://www.se.com/in/en/faqs/FA221785/

In case, for example if you have 6 devices with RS485 network length greater than 1200 meters then you must  use Modbus repeater in between the network.

 
Regards
Udhayakumar A K
ESXP System Support Expert

See Answer In Context

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-11-28 02:32 AM . Last Modified: ‎2023-11-28 02:38 AM

0 Likes
0
2823
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-28 02:32 AM

Hello @SESA528 , 

The more devices you will add, the more you need to be careful with the Timeout settings.

As mentioned by Guillaume, pay attention to the Modbus Master's requests on the 32 slaves.

 

Please have a look on the ULP System Guide:

  • https://product-help.schneider-electric.com/ED/ES_Power/ULP_System_IEC_Guide/EDMS/DOCA0093EN/index.h...
  • https://product-help.schneider-electric.com/ED/ES_Power/ULP_System_IEC_Guide/EDMS/DOCA0093EN/index.h...

This guide gives also some recommendation regarding IFM Modbus communication (also true for any other Serial Device chained to a gateway):

In terms of Modbus communication, it depends on the performance requirement. As it takes approximately 500 ms at 19,200 Baud per device to refresh 100 registers, the more interfaces added the longer the minimum refreshment period. The minimum refreshment period depends on the number of IFM interfaces stacked to one IFE server. Multiply the time to refresh one device by the number of devices to find the minimum refreshment period expected in the application. For instance, an installation with 8x IFM interfaces stacked to one IFE server at 19,200 Baud would take approximately 4 seconds to be read.

 

500 ms = performances for a breaker connected to an IFM. Will be lower (or worst ?!) depending on the connected device. 

 

You can also read the following Tech Notes dedicated to the Com'X510 to have some inspiration:

  • https://www.se.com/be/fr/download/document/ComX510_Gateway_Response_Calc_Tool_STN/
  • https://www.se.com/uk/en/download/document/ESXP1G001EN/

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Replies 7
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2023-11-23 09:10 PM

1 Like
0
2869
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-23 09:10 PM

Hello,

 

PAS support 32 serial devices when connected without modbus repeater. Pay attention to the performance as it is modbus serial. You have to take into account speed, type of device, number of register / frames to be recovered, time for the PAS and Device to return the modbus communication media.

 

Reply
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: ‎2023-11-24 12:55 AM

1 Like
0
2864
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-24 12:55 AM

Hi @SESA_B 

 

Adding to @Guillaume_Evrard comments, PAS can support up to 32 devices without repeater if the slave devices & RS485 wiring are as per the standard. Please refer this guidance for more information's and follow the wiring recommendations highlighted for better performance. https://www.se.com/in/en/faqs/FA221785/

In case, for example if you have 6 devices with RS485 network length greater than 1200 meters then you must  use Modbus repeater in between the network.

 
Regards
Udhayakumar A K
ESXP System Support Expert
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2023-11-24 03:58 AM

0 Likes
0
2856
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-24 03:58 AM

HI @UdhayakumarAK ,

 

Yes. Thanks very much.

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-11-24 04:50 AM

1 Like
1
2854
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-24 04:50 AM

Hello @SESA528 

As mentioned by  @UdhayakumarAK  the theoretical length of a Modbus serial line is 1200 meters/4000 feets...and more with repeaters.

However, this long bus length requires a lot of care and rigor for the cabling (cable impedance, connection of terminal blocks, etc.) and can be difficult to commission and to maintain.

So it might be a good idea to look at another solution based on Ethernet cables/networks, optical fibers between the cabinets / archi splitted on several Panel Server for a more robust architecture.

Moreover, it states in the Panel Server instruction sheet (JYT244902 for PAS800 / GDE7411905 for PAS600) that all cables wired to the Panel Server must be connected to a single building ground....not really possible when the length of the bus is 1200 meters (screenshot hereunder.

 

PaS hearting connection).png

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2023-11-27 12:40 AM

0 Likes
0
2833
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-27 12:40 AM

Hi @Thierry_Baudard ,

 

Okay thanks for your information. i will notice.

Reply
Romain_Polette
Spock Romain_Polette Spock
Spock

Posted: ‎2023-11-28 02:32 AM . Last Modified: ‎2023-11-28 02:38 AM

0 Likes
0
2824
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-11-28 02:32 AM

Hello @SESA528 , 

The more devices you will add, the more you need to be careful with the Timeout settings.

As mentioned by Guillaume, pay attention to the Modbus Master's requests on the 32 slaves.

 

Please have a look on the ULP System Guide:

  • https://product-help.schneider-electric.com/ED/ES_Power/ULP_System_IEC_Guide/EDMS/DOCA0093EN/index.h...
  • https://product-help.schneider-electric.com/ED/ES_Power/ULP_System_IEC_Guide/EDMS/DOCA0093EN/index.h...

This guide gives also some recommendation regarding IFM Modbus communication (also true for any other Serial Device chained to a gateway):

In terms of Modbus communication, it depends on the performance requirement. As it takes approximately 500 ms at 19,200 Baud per device to refresh 100 registers, the more interfaces added the longer the minimum refreshment period. The minimum refreshment period depends on the number of IFM interfaces stacked to one IFE server. Multiply the time to refresh one device by the number of devices to find the minimum refreshment period expected in the application. For instance, an installation with 8x IFM interfaces stacked to one IFE server at 19,200 Baud would take approximately 4 seconds to be read.

 

500 ms = performances for a breaker connected to an IFM. Will be lower (or worst ?!) depending on the connected device. 

 

You can also read the following Tech Notes dedicated to the Com'X510 to have some inspiration:

  • https://www.se.com/be/fr/download/document/ComX510_Gateway_Response_Calc_Tool_STN/
  • https://www.se.com/uk/en/download/document/ESXP1G001EN/

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
SESA528
Commander SESA528 Commander
Commander

Posted: ‎2023-12-01 12:13 AM

0 Likes
0
2805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-01 12:13 AM

Hi @Romain_Polette ,

 

Yes. Thanks very much. This is helpful information.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of