Reset of TH110 Sensors

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Reset of TH110 Sensors
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
Panel Server Entry

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Alexander_Akulov
Crewman Alexander_Akulov Crewman
Crewman

Posted: ‎2025-03-27 05:13 AM

0 Likes
8
1318
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 05:13 AM

Reset of TH110 Sensors

Hello, 

 

Currently we are changing ZBRN concentrators to PAS600. The main question is how to reset(unpair) TH110 sensors in order to pair them to newly installed PAS600


  • Thumbnail of Panel Server Entry
    Schneider Electric
    Panel Server Entry
View products (1)
Labels
  • Labels:
  • Commissioning
  • Legacy Gateways & Energy Servers
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-03-27 11:03 PM

1 Like
4
1286
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 11:03 PM

Hello @Alexander_Akulov 

 

ZBRN can not unpair a TH110, it can only delete the TH110 from its config but the sensor remained paired forever.

As of today there is not handy procedure except the empirical one which is not doable on real set-up. It is recommended to replace all TH110 by new ones paired to the PAS.

PAS like PTL have the capability to unpair the sensor ( delete = unpair if sensors are communicating with the PAS)

Kind Regards

See Answer In Context

Reply
Replies 8
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-03-27 08:45 AM

0 Likes
0
1300
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 08:45 AM

Hello @Alexander_Akulov , 


Please unpair the TH110 from the ZBRN gateway first. This will "release" the TH110 and enable them to be paired with a Panel Server. Refer to the ZBRN user manual.

 

If you do not follow this procedure, this will be very difficult to pair the TH110 with Panel Server.

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-03-27 11:03 PM

1 Like
4
1287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 11:03 PM

Hello @Alexander_Akulov 

 

ZBRN can not unpair a TH110, it can only delete the TH110 from its config but the sensor remained paired forever.

As of today there is not handy procedure except the empirical one which is not doable on real set-up. It is recommended to replace all TH110 by new ones paired to the PAS.

PAS like PTL have the capability to unpair the sensor ( delete = unpair if sensors are communicating with the PAS)

Kind Regards

Reply
Alexander_Akulov
Crewman Alexander_Akulov Crewman
Crewman

Posted: ‎2025-03-27 11:28 PM

0 Likes
1
1284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 11:28 PM

Hello @Guillaume_Evrard,

 

The equipment is already assembled. We have 292 sensors in total. It will be extremely hard to change 30% of sensors without disassembling. In case there is even a little chance that empirical way that may be applied to release sensors will work, we would like to try. Could you please share your experience with us  about any known possibilities to reset sensors?

 

Really appreciate you support.

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-03-27 11:33 PM

0 Likes
0
1282
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-03-27 11:33 PM

Hello,

Can you reach out to me please ?

Kind Regards

Reply
Luca_Rottoli
Luca_Rottoli Cadet
Cadet

Posted: ‎2025-10-20 05:54 AM

0 Likes
1
435
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-20 05:54 AM

Hi @Guillaume_Evrard , are there any news about TH110 sensor unpairing? I accidentally deleted the configuration from ZBRN and now I need to re-pair all the TH110 sensors. Is there a way to un-pair the sensors and reset them to 'Ready to pair' mode? Thanks in advance

Reply
javier.mayo
Crewman javier.mayo Crewman
Crewman

Posted: ‎2025-10-21 12:04 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-21 12:04 AM

Hi, don't you have a backup of zbrn32?

Reply
javier.mayo
Crewman javier.mayo Crewman
Crewman

Posted: ‎2025-10-21 12:11 AM

0 Likes
0
418
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-21 12:11 AM

If you don't have a ZBRN backup, the only solution is to unpair the TH110 sensors by injecting 20 amps for 20 minutes to the TH110 sensors, and then wait 3 minutes before pairing again.

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2025-10-21 10:32 PM

0 Likes
0
405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-21 10:32 PM

hello,

I reached out to Luca.

 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore