Replacement of EGX200MG to PAS600

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Replacement of EGX200MG to PAS600
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Nima101
Nima101
Cadet

Posted: ‎2025-05-15 07:13 PM

0 Likes
4
389
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 07:13 PM

Replacement of EGX200MG to PAS600

Hi all

I am trying to replace EGX200 with PAS600. We have 2 PMPs connected to the EGX200 via RS485 and it sends data to our PLC(concept). My question is what is the procedure to replace EGX to PAS600? we need to configure the PAS600? Do we need to change any Codes or Configuration in the PLC side?

 

 

 

Thanks

Labels
  • Labels:
  • Commissioning
  • Product selection
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-05-20 06:38 AM

1 Like
1
334
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 06:38 AM

Hello @Nima101 , 

Are you using COM1 and COM2 ports on your EGX200 ? One device on each COM port ?

 

If yes, we do not have recent gateway with 2 integrated ans separate RS485 ports. You can replace EGX200 by a Panel Server PAS600, but you will need to daisy chain your Modus Serial devices before connecting them to the RS485 port of the PAS600.

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-05-21 10:53 PM

0 Likes
0
292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-21 10:53 PM

hello @Nima101 

As explained by Eric transparent gateway should match, to use transparent gateway you just need to set the RS485 serial communication to your device ( baudrate, parity, data bit, stop bit). No need to add devicesin the PAS. PAS needs to have the modbus server enabled on the Eth port you are connected (by default on both ports in case of switched port).

For modbus RTU to modbus tcp gateway, Serial port has to remain by default (client mode) not reverse gateway (server mode).

As explained by Romain as PAS is having only one serial port you will have to daisy chain your 2 devices on the same RS485 network ( PAS support only 3 wires RS485) or use a passive serial splitter.  I do not know EGX200 but I have the feeling that COM1 and COM2 are splitted.

If your devices were having the same modbus ID  (not sure of the EGX200 configuration on serial ports if it is splitted or not ) you will have to change one of the 2 to avoid conflict.

If you had 2 different modbus ID, and the same serial config on the 2 ports and the same IP address for your EGX200, there will be no change as soon as the IP address of the PAS is using the IP address of the former EGX.

Your 2 devices will be available at PAS IP address : ID device 1 and PAS IP address : ID device 2

 

Kind Regards

See Answer In Context

Reply
Replies 4
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2025-05-15 11:18 PM

0 Likes
0
387
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-15 11:18 PM

Hello @Nima101 
It s seems that the Transparent gateway mode match your usecase:
Extract from PaS User Guide:

Eric_HAVAS_0-1747376287313.png

 

 

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-05-20 06:38 AM

1 Like
1
335
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 06:38 AM

Hello @Nima101 , 

Are you using COM1 and COM2 ports on your EGX200 ? One device on each COM port ?

 

If yes, we do not have recent gateway with 2 integrated ans separate RS485 ports. You can replace EGX200 by a Panel Server PAS600, but you will need to daisy chain your Modus Serial devices before connecting them to the RS485 port of the PAS600.

Regards, 

 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Nima101
Nima101
Cadet

Posted: ‎2025-05-20 11:23 PM

0 Likes
0
311
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-20 11:23 PM

Thank you for replying.

so, I just need to daisy chain them and put their serial address in the PAS600 config? Do I need to change anything in PLC side(Concept)?

Thanks

Nima

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-05-21 10:53 PM

0 Likes
0
293
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-05-21 10:53 PM

hello @Nima101 

As explained by Eric transparent gateway should match, to use transparent gateway you just need to set the RS485 serial communication to your device ( baudrate, parity, data bit, stop bit). No need to add devicesin the PAS. PAS needs to have the modbus server enabled on the Eth port you are connected (by default on both ports in case of switched port).

For modbus RTU to modbus tcp gateway, Serial port has to remain by default (client mode) not reverse gateway (server mode).

As explained by Romain as PAS is having only one serial port you will have to daisy chain your 2 devices on the same RS485 network ( PAS support only 3 wires RS485) or use a passive serial splitter.  I do not know EGX200 but I have the feeling that COM1 and COM2 are splitted.

If your devices were having the same modbus ID  (not sure of the EGX200 configuration on serial ports if it is splitted or not ) you will have to change one of the 2 to avoid conflict.

If you had 2 different modbus ID, and the same serial config on the 2 ports and the same IP address for your EGX200, there will be no change as soon as the IP address of the PAS is using the IP address of the former EGX.

Your 2 devices will be available at PAS IP address : ID device 1 and PAS IP address : ID device 2

 

Kind Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of