Greetings All,
I am looking for the practical cable distance limit of an RS-485 Daisy Chain through EtherGate.
My current understanding is that the device limit is roughly a third of the standard 32 devices (6-10), however I could not find any practical documentation on Cable Distance in real-world applications, and am sure that it will be less than 4000m - the standard for RS-485.
Regards, Scott.
Link copied. Please paste this link to share this article on your social media post.
For your convenience, in the future please place your question in the corresponding sub community as more people will see it there. This question had been placed in "Community Help", and only people following this sub Community will get notified. You find the sub communities in the top left part. Click "Communities" and then select the area your question is about.
I've moved this question for you.
Posted: 2017-12-01 03:40 AM
Link copied. Please paste this link to share this article on your social media post.
Hi Scott,
According to my knowledge the device limit is 32 device on paper but for practically it is recommended to use
Up to 25-30 device on single daisy chain loop without any repeater to avoid disturbance and fluctuation of data.
And if we are talking about cable distance in real time application it is 4000 feet i.e.,around 1200 m.
Regards,
Abbyshek
Link copied. Please paste this link to share this article on your social media post.
The maximum length of the daisy chain is dependent on the baud rate of the devices.
Typical maximum RS-485 Drive Distance
| Baud Rate | 150-9600 | 19200 | 38400 | 57600 | 115200 |
| Distance (feet) | 4000 | 3200 | 3000 | 2300 | 1600 |
| Distance (meters) | 1220 | 975 | 914 | 701 | 488 |
*Note: Based on 24 AWG twisted shielded pair, 0.026 Ohm/ft (0.085 Ohm/m), 13pF/ft(41pF/m) conductor to conductor, 22 Pf/ft (72pF/m) conductor to shield.