I've tested both CL110 and TH110 with PowerTag Link with w1.4.5. I have not tried with latest fw 1.6.7 (I will be able to access to my Lab only after the lockdown...).
What is the current flowing through the ferromagnetic ribbon of the TH110 ? Theoretically You need to have 5 Amps but I strongly recommend to have 10 Amps if your TH110 is far away from the Powertag Link. There is no LED or indicator on the TH110 that allow to know if it is active.
Once the TH110 is powered on, you will discover it under the PowerTag Link Web Interface or with EPC.
Regards.
Romain POLETTE Solution Architect - France Operations