Ask Me About Webinar: Data Center Assets - Modeling, Cooling, and CFD Simulation Join our 30-minute expert session on July 10, 2025 (9:00 AM & 5:00 PM CET), to explore Digital Twins, cooling simulations, and IT infrastructure modeling. Learn how to boost resiliency and plan power capacity effectively.Register now to secure your spot!
Powertag link HD with TH110
Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
I've tested both CL110 and TH110 with PowerTag Link with w1.4.5. I have not tried with latest fw 1.6.7 (I will be able to access to my Lab only after the lockdown...).
What is the current flowing through the ferromagnetic ribbon of the TH110 ? Theoretically You need to have 5 Amps but I strongly recommend to have 10 Amps if your TH110 is far away from the Powertag Link. There is no LED or indicator on the TH110 that allow to know if it is active.
Once the TH110 is powered on, you will discover it under the PowerTag Link Web Interface or with EPC.
Regards.
Romain POLETTE Solution Architect - France Operations