Hi all,
I use com'X 210 log data, meet error code 19.
what kind of error is this?
thanks.
Link copied. Please paste this link to share this article on your social media post.
HI,
From my experience, it is the same Error 19 code as for EGX300:
Link copied. Please paste this link to share this article on your social media post.
Hi,
In the Com'X 210/510, the error code 19 just means an error occured. It doesn't have a specific meaning. It may be helpful to check the communication diagnostic table onboard the Com'X to determine the error. This is located under the Diagnostics tab -> Modbus. Then select "Device Details".
Randi