I am looking for powerTag link 100 Modbus Mapping address for TH110 & CL110, Sensor configuration need guidance & support for same.
Link copied. Please paste this link to share this article on your social media post.
Hello @VineetKushwaha ,
You can have a look on the Panel Server Modbus file. Environnemental data are the same.
Com'X User Manual also listed the registers:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @VineetKushwaha ,
You can have a look on the Panel Server Modbus file. Environnemental data are the same.
Com'X User Manual also listed the registers:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello,
I confirm @Romain_Polette 's reply, same register between PAS and PTL in case of One sensor = one modbus device, for PTL there is a synthesis table to allow having all the temperature and humidity on one modbus ID with 1st sensor, 2nd sensor, etc... Table is refreshed/updated if you delete the 2nd sensor as an example. This feature does not exist yet in PAS.
There is an excel spreadsheet but not sure we are allowed to disclose. Would suggest to ask Thierry Baudart