Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Categories
  • Forums
  • Knowledge Center
  • Blogs
  • Ideas
  • Events & Webinars
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

Panel server PASS600 actualización de firmware

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel server PASS600 actualización de firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Levy90
Ensign Levy90
Ensign

Posted: ‎2025-10-01 04:25 PM

0 Likes
5
782
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-01 04:25 PM

Panel server PASS600 actualización de firmware

Hola 

Tengo un panel server (PAS600) con version del firmware 1.0.0 y al conectarme al equipo de forma física y entrar al equipo e ir a la parte de actualización del firmware deben aparecer 3 botones descargar, importar e instalar, pero en este equipo solo aparecen importar e instalar así que importamos el archivo que habíamos descargado e instalado en otros equipos, pero marca error. ¿Qué es lo que puedo hacer?

 

Tengo otro PAS600 que tenía la v2.0.0 de fábrica y en todos se pudieron actualizar, pero excepto este dispositivo que tiene v1.0.0

 

Muchas gracias por su aporte

Tags (4)
  • Tags:
  • english
  • firmware
  • Panel Server
  • PAS600
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-10-06 02:23 AM . Last Modified: ‎2025-10-16 06:19 AM

0 Likes
0
714
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-06 02:23 AM

Hello @Levy90 , 

"cargar archivo" is a feature that is not available with 001.006.000.

Because you are in 001.006.000 Hardware version of the Panel Server is not displayed in the "Informacion de Firmware" page => this PAS600 has Hardware is V1.0 because HW v2.0 was released with V002.001.000.

 

Please check this page for more info abour HW version and how to know the HW version of your PAS600:

https://www.productinfo.schneider-electric.com/ecostruxurepanelserverguide/doca0172-ecostruxure-pane...

 

Maybe the FW version your downloaded through the Web pages of the other PAS600 (HW 2.0 ???) is not compatible with this one.

 

Better upgrade your Panel Server with EcoStruxure Power Commission. 

 

Regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Reply
Levy90
Ensign Levy90
Ensign

Posted: ‎2025-10-16 08:21 AM

0 Likes
0
566
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-16 08:21 AM

Sí una disculpa por no informar de la situación, pero ya se pudo instar la version del firmware del dispositivo iEM3255 con v1.0 y se pudo a través del power commission sin nigun problema.

 

Muchas gracias por su apoyo y comentarios fueron de mucha ayuda.

See Answer In Context

Reply
Replies 5
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-10-02 02:59 AM

0 Likes
1
775
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-02 02:59 AM

Hello @Levy90 , 

 

FW 001.000.000 never existed for Panel Server (except for demo products).


Can you share a screenshot of your FW page ?

 

Thanks.

 

Romain POLETTE
Solution Architect - France Operations
Reply
Levy90
Ensign Levy90
Ensign

Posted: ‎2025-10-03 11:04 AM

0 Likes
0
745
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-03 11:04 AM

Hola @Romain_Polette 

 

Gracias por tu aporte, tengo una foto, pero salió poco movida

Firmware iEM3255.png

 En la parte de abajo se aprecia el botón de cargar archivo, pero en los otros dispositivos si aparecía el de descargar, y cargábamos el archivo que se había descargado en los anteriores y marcaba error.

Attachments
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-10-06 02:23 AM . Last Modified: ‎2025-10-16 06:19 AM

0 Likes
0
715
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-06 02:23 AM

Hello @Levy90 , 

"cargar archivo" is a feature that is not available with 001.006.000.

Because you are in 001.006.000 Hardware version of the Panel Server is not displayed in the "Informacion de Firmware" page => this PAS600 has Hardware is V1.0 because HW v2.0 was released with V002.001.000.

 

Please check this page for more info abour HW version and how to know the HW version of your PAS600:

https://www.productinfo.schneider-electric.com/ecostruxurepanelserverguide/doca0172-ecostruxure-pane...

 

Maybe the FW version your downloaded through the Web pages of the other PAS600 (HW 2.0 ???) is not compatible with this one.

 

Better upgrade your Panel Server with EcoStruxure Power Commission. 

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-10-15 12:51 AM

0 Likes
1
583
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-15 12:51 AM

Hello @Levy90 , 


Any news ?

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Levy90
Ensign Levy90
Ensign

Posted: ‎2025-10-16 08:21 AM

0 Likes
0
567
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-10-16 08:21 AM

Sí una disculpa por no informar de la situación, pero ya se pudo instar la version del firmware del dispositivo iEM3255 con v1.0 y se pudo a través del power commission sin nigun problema.

 

Muchas gracias por su apoyo y comentarios fueron de mucha ayuda.

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore