Hi Xperts,
We have a panel server (PAS800) that is refusing the firmware updates via self webpage and EPC.
We have tried resetting to factory and still no success in updating the firmware.
Current Firmware is 001.006.000
Update via webpage – It is saying “Bundle Invalid Signature” (We have tried hardware V1 and hardware v2 with same results). The PAS does not have a physical print of which HW it is so we are assuming it is HW1
Via EPC - Upgrade Unsuccessful
Thanks in advance
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
Ensure that the time is correct on your PAS before doing the upgrade.
For sure this is HW V1, HW V2 is only available with 2.0.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Hello @jedzruiz1985
Ensure that the time is correct on your PAS before doing the upgrade.
For sure this is HW V1, HW V2 is only available with 2.0.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Hi Guillaume,
All good now! it was the clock. Previous commissioning we had didn't need to set the clock first when updating the firmware.
Thanks very much!
Best regards