Hi team,
Is there an official list of downstream devices (mainly interested in meters) that can be displayed on FDM128 via a Panel Server?
I noticed in the manual that the FDM would display information for iEM2000/3000 when connected through the Smartlink SIB but it says only PowerTag is supported through Panel Server.
Link copied. Please paste this link to share this article on your social media post.
Hello @DeanZouganelis ,
Devices supported by FDM128 are listed in the user manual.
This remote screen was originally released to display information of 8 breakers. Later, the device was adapted to display information from Acti 9 system (Smartlink, OF/SD, Reflex iC60, RCA).
Listed energy meters (iEM2000, iEM3000) are compatible with FDM128 but only when pulse output of these meters is connected to an input of a Smartlink. iEM are not supported when connected through direct Modbus to FDM128.
Finally, FDM128 was upgraded to display PowerTag energy sensors => gateway for PowerTag can be:
Check if your FDM128 has latest FW uploaded:
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @DeanZouganelis ,
Devices supported by FDM128 are listed in the user manual.
This remote screen was originally released to display information of 8 breakers. Later, the device was adapted to display information from Acti 9 system (Smartlink, OF/SD, Reflex iC60, RCA).
Listed energy meters (iEM2000, iEM3000) are compatible with FDM128 but only when pulse output of these meters is connected to an input of a Smartlink. iEM are not supported when connected through direct Modbus to FDM128.
Finally, FDM128 was upgraded to display PowerTag energy sensors => gateway for PowerTag can be:
Check if your FDM128 has latest FW uploaded: