Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
2024-12-1609:32 PM
Panel Server as a gateway for FDM128
Hi team,
Is there an official list of downstream devices (mainly interested in meters) that can be displayed on FDM128 via a Panel Server?
I noticed in the manual that the FDM would display information for iEM2000/3000 when connected through the Smartlink SIB but it says only PowerTag is supported through Panel Server.