Hi Expert,
Is there a way to adjust the content of SFTP? I connected CL110 sensor, in Publishing SFTP can show temperature and humidity. If i want to Publishing the other data say Battery level and RSSI, is it possible to do that?
Link copied. Please paste this link to share this article on your social media post.
Hello @sesa448029_brid ,
It seems that the native CL110 model does not have Battery Level and RSSI data.
You need to create a custom model.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Romain,
Thanks for your reply, i checked on manual the custom model only support Modbus serial/TCPIP, CL110 is wireless devices connect by zigbee, is there anyway i can use custom model for this device?
Link copied. Please paste this link to share this article on your social media post.
Hi @sesa448029_brid ,
CL110 requires a wireless gateway such as Panel Server PAS400/PAS600/PAS800 (output protocol = Modbus TCP). Please check Panel Server Modbus file to have Modbus table related to CL110.
If you have a Modbus table, you can create a Custom Model for Panel Server by connecting to the EPC Web portal:
https://portal.cloud-commissioning.se.com/portal
As a Schneider internal, you should have access to this portal.
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Romain,
I tried to create custom model and import to panel server, If I want to achieve my goal- CL110 Temp, humidity, Battery level, RSSI these 4 data via Panel Sever SFTP to Third party platform, my understanding need 2 panel server
1. Panel server A connect all wireless sensor (CL110), then enable modbus TCP/IP by switched or Wifi.
2. Panel server B import custom mode file with these 4 parameter via modbus TCP/IP polling panel server A with sensor virtual ID.
3. Finally Panel server B use SFTP function publication these data to third party platform.
i tried Panel server A polling it's self IP but it's not work due to "Invalid IPv4 settings", but i haven't try if ethernet port 1 polling ethernet port 2, only tried wifi at the panel server from now only connect by wifi.
Link copied. Please paste this link to share this article on your social media post.
Hi @sesa448029_brid ,
You got a point.
Custom Models cannot be applied directly to a wireless device because you do not have possibility to add a wireless device manually and associate a specific device type like Modbus devices.
Wireless devices connected to "Child Gateway" will be considered as Modbus TCP device by "Mother Gateway". In this case, this may me possible to manually add a CL110 on the Mother Gateway and associate a custom device type.
Connecting CL110 to some PAS400 and use PAS600/800 as a data concentrator for SFTP publication is a possible architecture. I never tested this configuration by this should work.
@Eric_HAVAS can you confirm if this configuration is working ?
Regards,