Panel Server Publication failing or data buffer near full

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server Publication failing or data buffer near full
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Spock Romain_Polette Spock
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2024-11-20 05:04 PM

0 Likes
3
381
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-20 05:04 PM

Panel Server Publication failing or data buffer near full

Hi All

 

Would like to inquire about an issue with the Panel Server 600 (Firmware 001.006.000). We've noticed an event log message "Publication failing or data buffer near full," and the LED indicator is continuously blinking orange. I have checked with the customer that all communication is working well and the PAS is not connected to the cloud.

 

Any suggestions on how to diagnose the device and resolve the issue? Thanks

 

Stuart_Cheng_0-1732151045264.png

 

Attachments
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-11-20 10:15 PM

0 Likes
0
365
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-20 10:15 PM

hello, if the PAS is used as a modbus tcp gateway, or not intended to log data, just disable publication and data sampling. If you are not pushing the data to SFTP, https, nor ETP with data sampling enabled you will fill in the buffer....

See Answer In Context

Reply
Replies 3
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-11-20 09:09 PM

0 Likes
0
371
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-20 09:09 PM

Hello @Stuart_Cheng ,

Are you publishing to ETP or not ? If yes and you have the cloud connection icon in red, this is normal to have a buffer full. I strongly recommend to upgrade to 2.0 as ETP connection has been improved.

You have to restore communication to ETP and let the PAS to empty the buffer, It can take a while.

To troubleshoot the connection issue either get a disgnostic from PAS or check network, publication settings.

 

 

Reply
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2024-11-20 10:06 PM

0 Likes
1
367
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-20 10:06 PM

Hi @Guillaume_Evrard 

 

Thanks for the reply.

I checked with the customer, and they confirmed that they are not publishing data to ETP. However, from the screenshot, I noticed that data sampling is in green. Could the event message indicate that the memory is full? If so, do you know how to clean the buffer in PAS?

Thank you!

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-11-20 10:15 PM

0 Likes
0
366
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-11-20 10:15 PM

hello, if the PAS is used as a modbus tcp gateway, or not intended to log data, just disable publication and data sampling. If you are not pushing the data to SFTP, https, nor ETP with data sampling enabled you will fill in the buffer....

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of