Panel Server - Known bugs by firmware

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150โ€ฆ

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results forย 
Showย ย onlyย  | Search instead forย 
Did you mean:ย 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server - Known bugs by firmware
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-08-01 06:59 PM . Last Modified: โ€Ž2023-10-29 03:08 PM

1 Like
15
2422
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-01 06:59 PM

Panel Server - Known bugs by firmware

Hello All,

To prevent others from falling into the same issues as we have with this range of devices, I have compiled a short list of bugs in the PAS firmware that we have encountered. These bugs are centered around file drop, accuracy of file timestamp logging and ETL. 

 

Firmware 1.7.0

This firmware changes the measurement naming for the IO devices, namely Smartlinks. This will break ETL integrations to PME and PSO. We have not confirmed whether this affects custom devices from the portal. 
For Example:

Old measurement name:   IoCountMeasurement (L)

New measurement name: (L)

 

Solution: Modify ETL mapping for the new measurements.

 

Firmware 1.6.0

  1. NTP functionality is working but not reporting in the web page correctly. Web page Reports 'OK' but the 'Last Date and Time Synchronization' does not update making it appear like it hasn't synced in a long time. Looking into the logs we can see it is syncing. The .CSV file drops are correctly timestamped but are in UTC+0 timezone.
  2. The .CSV format issue. The PAS .CSV file includes "" around every field. This causes all sorts of issues to .CSV extractions tools such as ETL. This was introduced in 1.6.0.

Firmware 1.5.1

  1. NTP functionality not working. Reports 'OK' but never syncs time. Even when a completely random manual IP is used it reports 'OK' ๐Ÿ™‚
  2. When a SmartLink is added, SFTP fails after 1-3 weeks. Appears to be centered around the PAS losing SmartLink settings (according to the PAS logs). Reboot will make file publication work again BUT without some SmartLink device names in .CSV file. Data extraction tools like ETL cannot process the files without a devices name.
  3. When the PAS network is set to 'Separated', the published file do not have a MAC therefore no valid start name for ETL to reference (you cant use ETL). Solution - update to newer firmware.

Firmware 1.5.0

  1. Same bugs as 1.5.1

 

NOTES:

A temporary work around for the 1.6.0 .CSV " format issue can be achieved using a PowerShell script and Window Task scheduler. It's not ideal and may be prone to fail when windows update.

Other minor issues:

  • Still no native support for Schneiders PM5350 meter after many firmware releases ๐Ÿ˜ž
  • The Time zone settings limited to 0+ UTC. Difficult to work with when you don't live in 0+ UTC
  • SFTP File publication only supports 1minute, 2 minutes, 10minutes and 1hour. There is no 15minute interval which is a standard logging interval.
  • When manually exporting data from the PAS800, the .CSV file format is incredibly hard to work with compared to the ComX510. Most customers cannot use the .CSV exports as the Panel Server in the way the marketing material suggests, but require either Energy Hub or PME to work with it.

 

Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 15
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: โ€Ž2023-08-11 04:17 AM

0 Likes
1
2362
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-11 04:17 AM

Hello @Sam_Vosch 

 

Thanks for highlighting these points. For NTP time sync issue, have you raised any customer support case? If not would recommend you to raise a support ticket with logs & screenshots.

For csv file format issue, as you mentioned temporary solution is to use the PowerShell script & this will be addressed at system level in ETL tool hotfix releasing this month end.

https://www.se.com/in/en/faqs/FAQ000259575/

 

Thanks & Regards

Udhay

Regards
Udhayakumar A K
ESXP System Support Expert
Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-08-13 01:57 PM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-13 01:57 PM

Hello UdhayakumarAK, thank you for your reply.

I raised the issues with Power Solutions Global Expert Technical Support weeks ago (logs included), and you replied to the issues. As you know from my latest reply, some of these issues are still ongoing as we find out more about the issues.

The main purpose of this post is to inform the wider community of the issues with the PAS devices. I have not seen a bulletin or post informing the community of the community of serious firmware issues that will compromise data into their PME/PSO systems. Hopefully this community post will help other Schneider partners and prevent others finding the same issues the hard way.

Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-08-13 02:02 PM

0 Likes
0
2344
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-13 02:02 PM

Further point on firmware 1.5.1: 

We found that Firmware 1.5.1, while it also has the same sync issues as 1.6, it does not add the UTC time offset to the .CSV file.

This can cause serious erroneous data entries into customer sites. Essentially, if ETL or similar applications are used, it will input the data 12 hours up to into the future (if you are in +12 GMT). 

Special care will need to be taken if the site uses consumption data for billing purposes.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: โ€Ž2023-08-15 10:24 PM

1 Like
2
2292
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-15 10:24 PM

Hello NTP is working well using 1.6, why are you saying it is not ? There was an issue with the SE NTP server, that should have been fixed.

Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-08-17 01:22 PM

0 Likes
1
2267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-17 01:22 PM

Hello Guillaume,
I have been working with support and it looks like NTP functionality is working but not Reporting in the web page correctly. Web page Reports 'OK' but the 'Last Date and Time Synchronization' does not update making it appear like it hasn't synced in a long time. Looking into the logs we can see it is syncing. The .CSV file drops are correctly timestamped but are in UTC+0 timezone.
I will update the original post.

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: โ€Ž2023-08-17 11:28 PM

1 Like
0
2253
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-08-17 11:28 PM

Hello Sam,
It s been reported in web page but only when time difference between PaS time and ntp time is signifiant.
Regarding CSV, the "" were added following customer complains regarding "special" characters used commonly in their country causing unexpecting behaviour in csv export of SFTP transfer.

Reply
CamboHeath
Lieutenant | EcoXpert Master CamboHeath Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-10-02 08:34 PM

0 Likes
1
2117
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-10-02 08:34 PM

I am encountering numerous issues with the NTP in both PAS600 and PAS800 gateways on Firmware 1.6.0. that line up with what Sam was seeing above. Can you please advise whether these issues are on the radar for resolution?

 

On one site i have several PAS800s and PAS600s that all say "Connection successful to NTP server", however I can see they are out of sync by at least several seconds, and due to daylight savings they are now an hour out of sync even though they say that the connection is successful. However on another site I will get "Connection failed to NTP server" regardless of if the devices sync to a NTP or the Schneider electric cloud. 

 

Please advise what the story is with getting NTP functioning and reporting correctly on Panel Servers.

 

 

 

 

 

 

 

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: โ€Ž2023-10-02 09:09 PM

0 Likes
0
2114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-10-02 09:09 PM

Hello,

 

Issues with NTP have been reported with 1.7 also. We had an issue over the last weeks with the SE NTP server (one used by SE Cloud) not responding and sometimes using an alternate NTP server can solve the issue. Remember to whitelist the url.

Normally you should be able to see the synch message in the log periodically. Today PAS is using UTC only, so not sure to understand the point with daylight saving,

 

Reply
CamboHeath
Lieutenant | EcoXpert Master CamboHeath Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-10-03 01:14 PM

0 Likes
1
2106
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-10-03 01:14 PM

Thanks for the reply Guillame. Just to confirm:

 

1. Should SE NTP currently be fully functional on 1.6?

2. Should Local Static NTP currently be fully functional on 1.6?

 

I have several PAS's on 1.6 all pointing to the same static NTP that all say "Connection successful to NTP server" but that clearly are not synced when a new minute rolls around on the NTP source and they all tick over at different times. None of my PAS's syncing to the SE NTP appear to be syncing either

 

Can you please confirm if the NTP should be fully functional on 1.6? Thanks

 

 

Reply
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: โ€Ž2023-10-18 01:22 AM

0 Likes
0
2084
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-10-18 01:22 AM

Hello @CamboHeath 

 

As mentioned by Guillame we had SE cloud NTP time sync issue in past weeks, and still there are some interim issues ongoing with cloud sync. And with respect to static NTP, we don't see any gap. Please raise a customer support ticket for further investigation with below details

1. Screen Capture of the time difference with respect to NTP server

2. Screen Capture of PAS Date & Time settings page 

2. PAS logs (both diagnostic & configuration logs)

But strongly suggest to upgrade the Panel server to the latest Firmware version.

Thanks & Regards

Regards
Udhayakumar A K
ESXP System Support Expert
  • Thumbnail of EcoStruxure Panel Server Universal
    Schneider Electric
    EcoStruxure Panel Server Universal
View products (1)
Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2023-10-29 03:12 PM

0 Likes
0
2042
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2023-10-29 03:12 PM

I have updated original post to include issue with Firmware 1.7.

Reply
Sam_Vosch
Lieutenant | EcoXpert Master Sam_Vosch Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: โ€Ž2024-01-10 07:29 PM

0 Likes
3
1719
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2024-01-10 07:29 PM

I think we have solved the NTP issues. When using a local static NTP server on a local network (such as 192.168.1.x), on either a closed managed network or an open unmanaged network, the PAS MUST have a static DNS address?

To me this is so strange. We are using a fixed local IP address which would never need a DNS to translate the IP to an IP. A DNS is mostly used to translate an address like 'google.com' to an IP address. It should not be needed or related to the issue, but I have confirmed that setting the DNS to the router's IP fixed the issue on 3 different sites.

The PAS will not even attempt to send a NTP request on the network when the DNS is not set statically (as proven when we used Wireshark on the network). But as soon as the static DNS is set, we can see the PAS sending NTP requests in Wireshark.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: โ€Ž2024-01-10 09:13 PM

0 Likes
1
1712
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2024-01-10 09:13 PM

Hello,

From what I understand the NTP server set in PAS is a static IP address and not a url. Correct ?

I understand also that setting an IP address (router or gateway adress)  even not being a DNS is working ?

Fully agree with you it should work, do you know if a defect has been raised ?

Kind Regards

Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: โ€Ž2024-01-11 11:05 PM

0 Likes
0
1679
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2024-01-11 11:05 PM

Hello Guillaume,
Yes before this post in se.com, Sam has already contacted the Customer Care Center, as it is the usual process for technical issues and the CCC took already into account his request which is currently being investigated by the panel server team.

Reply
UdhayakumarAK
Commander UdhayakumarAK Commander
Commander

Posted: โ€Ž2024-02-20 08:48 PM

0 Likes
0
1501
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

โ€Ž2024-02-20 08:48 PM

Hello Sam @Sam_Vosch 

This is addressed in FW 001.009.000, suggest you to update the FW to resolve this issue.

Regards
Udhayakumar A K
ESXP System Support Expert
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

ย 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings ยฉ 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of