A customer has provided an address of 105.193.211.255 to assign as the IP of a PAS. I am aware that in some instances this is not possible, as x.x.x.255 can be reserved as a broadcast address.
For example, 105.193.211.0/255.255.255.0
The network identifier would be 105.193.211.0
The broadcast address would be 105.193.211.255
Valid (or usable) ip addresses would be 105.193.211.1 to 105.193.211.254
However in an expanded network (Class A/B), I was under the assumption that this should be possible.
For example, 105.193.211.0/255.255.0.0
The network identifier would be 105.193.0.0
The broadcast address would be 105.193.255.255
Valid (or usable) ip addresses would be 105.193.0.1 to 105.193.255.254
When I am testing this on a PAS, it fails to save an IPV4 address ending in .255 regardless of the subnet. Am I missing something obvious? Or misunderstanding the capabilities here? Thanks.
Link copied. Please paste this link to share this article on your social media post.
Hello,
As you mentioned, an all IPV4@ ended terminated by 255- in a /16 or larger subnet should not be prohibited .
But today the control of the value entered is simplified and all IP@ ending in 255 are prohibited regardless of the value of the mask.
The workaround today is to set another IP@ not terminated with 255. This should be possible due to the larger number of IP@s available in a class A/B subnet.
Link copied. Please paste this link to share this article on your social media post.
I am no PAS expert, but I suspect 255 is reserved for historical reason https://www.se.com/us/en/faqs/FA222364/
Link copied. Please paste this link to share this article on your social media post.
IP Address: 105.193.0.0/16
Network Address: 105.193.0.0
Usable Host IP Range: 105.193.0.1 - 105.193.255.254
Broadcast Address: 105.193.255.255
Total Number of Hosts: 65,536
Number of Usable Hosts: 65,534
Subnet Mask: 255.255.0.0
In theory, the PAS should be able to recognise /16 and allow IP assignment within any of the Usable Host IP range as above.. however seem like any IP ending with .255 is given this error.
Link copied. Please paste this link to share this article on your social media post.
hello,
This is what I remember 0 is the network address and 255 is the brodcast address if you have /24 subnet.
Link copied. Please paste this link to share this article on your social media post.
Hello,
As you mentioned, an all IPV4@ ended terminated by 255- in a /16 or larger subnet should not be prohibited .
But today the control of the value entered is simplified and all IP@ ending in 255 are prohibited regardless of the value of the mask.
The workaround today is to set another IP@ not terminated with 255. This should be possible due to the larger number of IP@s available in a class A/B subnet.
Link copied. Please paste this link to share this article on your social media post.
Thanks for the response. This is what I was expecting.