Panel Server/Com´X with separate eth ports settings and two system

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Panel Server/Com´X with separate eth ports settings and two system
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
AndersDahlskog
Lieutenant AndersDahlskog Lieutenant
Lieutenant

Posted: ‎2023-01-30 06:39 AM

0 Likes
6
1329
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-30 06:39 AM

Panel Server/Com´X with separate eth ports settings and two system

Hi

Can two system on different data LAN networks "use" same gateway (Panel Server/Com´X) and the modbus slaves connected to it ?

One system Resorce Advisor is connected to port ETH 1 with it´s own LAN network and a second system Power Monitoring Expert is connected to port ETH 2 with a different LAN network.

 

BR/Anders

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Labels
  • Labels:
  • Product selection
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-02-01 05:30 AM

1 Like
0
1242
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-01 05:30 AM

 

Capture.JPG

 

Just need to enable modbus services on port 2 ( modbus server functionnality on port 2) 

See Answer In Context

Reply
Replies 6
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-01-30 07:28 AM . Last Modified: ‎2023-01-30 07:30 AM

0 Likes
0
1297
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-30 07:28 AM

Hello @AndersDahlskog , 

The goal of separated ETH ports is to segregate downstream Modbus TCP/IP devices connected to ETH2 port from upstream communication systems connected to ETH1 port.

I'm not sure about the PAS behavior if it detects trafic on ETH2 related to the PME server polling. Normally PAS must initiate first trafic on ETH2 (because a Master is polling on ETH1). Wondering if some CyberSec rules in the PAS can have an impact.

=> Need confirmation of an expert 🙂

 

If your PME Server has the same IP range than ETH2 of Panel Server (PAS) and downstream devices, this should work (in theory):

  • PAS will poll data of devices connected to ETH2 and push data on Resource Advisor
  • PME Server will poll devices that are on its same IP range


In this case the PAS is no use for PME Server:

  • Resource Advisor will use the Virtual ID attributed to the devices by the PAS.
  • PME will not use the Virtual ID as recommended by the User Manual.

 

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-01-30 09:02 AM

0 Likes
2
1289
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-30 09:02 AM

Hello,

 

To avoid overloading the Panel Server CPU, only temporary connections (such as viewing web pages) are validated in addition to a permanent client connection (such as PME or an SE cloud advisor).
Dual connection of two permanent upper clients as you mention is not within the framework of the possible and validated architecture and is therefore not supported

BR

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
AndersDahlskog
Lieutenant AndersDahlskog Lieutenant
Lieutenant

Posted: ‎2023-01-30 10:27 PM

0 Likes
1
1267
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-30 10:27 PM

Hello

Thanks for answer, is it the same regarding Com´X210, Com´X510 ?

BR/Anders

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-01-30 11:22 PM . Last Modified: ‎2023-01-30 11:25 PM

0 Likes
0
1256
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-30 11:22 PM

Hello,

What you need is the serial modbus gateway on port 2 ( enabled by Default on COMX but not on PAS in seggregated ports) and basically you are using the cloud connectivity on Port 1.

COMX/PAS will poll the devices for the data to be pushed to RA.

Only limitation is the number of devices and the capacity of the gateway to act as Modbus gateway and a cloud gateway simultaneously but It should work with PAS as working with COMX.

Without any serial modbus this is what we are doing in Asset Advisor ED with "electrical LAN " and PME on port 2 and port 1 to cloud.

 

PAS and COMX in seggregated modes are able to poll modbus tcp devices on both ports (ie on different LAN segment).

Reply
AndersDahlskog
Lieutenant AndersDahlskog Lieutenant
Lieutenant

Posted: ‎2023-01-31 01:39 AM

0 Likes
1
1250
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-01-31 01:39 AM

Hi

We have a PAS with 20 connected serial RS485 devices.  Port 1 goes to an existing RA and we would like to connect a new PME system to port 2 to read the data from the same devices. I am aware of the limitations mentioned above.

Can port 2 be enabled for serial modbus gateway on PAS as defult in Com´X

Would this scenario be possible?

BR/Anders

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-02-01 05:30 AM

1 Like
0
1243
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-01 05:30 AM

 

Capture.JPG

 

Just need to enable modbus services on port 2 ( modbus server functionnality on port 2) 

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore