Hi everyone!
I'd like to ask you about a problem with a PAS800L and some PM5560 meters. There are 20 meters in the system but we can't see some parameters of 2 of them. It does not log these parameters neither. The both of them have a direct connection to the switch (no daisy chain).
Any idea of what causes this?
Thank you!
Link copied. Please paste this link to share this article on your social media post.
Hello @Veronika.Salinas ,
It seems that real time data are not available... did you check with a 3rd party modbus tool to verify that these values are at least available through Modbus ?
In your case, you have Total Active Power, but an issue reading Active Power per phase.
Does your PM5560 parameters are the same for all your meters ? Check these PM5000 are not set in 1PH wiring mode.
Did you check that device type you set in the Panel Server matchs the real device commercial ref ?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hello @Veronika.Salinas ,
It seems that real time data are not available... did you check with a 3rd party modbus tool to verify that these values are at least available through Modbus ?
In your case, you have Total Active Power, but an issue reading Active Power per phase.
Does your PM5560 parameters are the same for all your meters ? Check these PM5000 are not set in 1PH wiring mode.
Did you check that device type you set in the Panel Server matchs the real device commercial ref ?
Regards,
Link copied. Please paste this link to share this article on your social media post.
Hi Romain
Thank you!
The wiring configuration was different than the others. The problem is solved.
Best regards.