Greetings everyone.
We have an installation that includes a PAS600 with a few Power Tags. We want to install a PAS800 as well.
Can we somehow send the Data Logging of the PowerTags to the PAS800? Basically, can we see the data from PAS600 in the PAS800?
Is it possible only with another PAS600, instead of PAS800?
Thank you in advance.
Link copied. Please paste this link to share this article on your social media post.
Hello @Konstantinos_Patsaris ,
Yes, you can view the data of devices below your PAS600 on a PAS800. This is done using the Parent / Child architecture. For you, the Parent is PAS800 and Child will be PAS600 gateway.
You will be able to find details about this architecture
* on this video (for example with demo2 around 01min57sec )
* or in the PaS user guide page 235.
The "concept" is to add your PAS600 devices on PaS800 gateway as modbus TCP/IP devices using IP of your PAS600 and using the virtualID for your PAS600 powertags devices.
Regards
Eric
Link copied. Please paste this link to share this article on your social media post.
Hello @Konstantinos_Patsaris ,
Yes, you can view the data of devices below your PAS600 on a PAS800. This is done using the Parent / Child architecture. For you, the Parent is PAS800 and Child will be PAS600 gateway.
You will be able to find details about this architecture
* on this video (for example with demo2 around 01min57sec )
* or in the PaS user guide page 235.
The "concept" is to add your PAS600 devices on PaS800 gateway as modbus TCP/IP devices using IP of your PAS600 and using the virtualID for your PAS600 powertags devices.
Regards
Eric