PAS800 Custom Device Model (for firmware 001.004.000)

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS800 Custom Device Model (for firmware 001.004.000)
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server Advanced

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
swil
Commander swil
Commander

Posted: ‎2022-09-23 07:19 PM . Last Modified: ‎2022-09-23 07:28 PM

1 Like
14
4834
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-23 07:19 PM

PAS800 Custom Device Model (for firmware 001.004.000)

Q1. Does PAS800 support end users having the ability to create/use  custom device models?

Q2. Please provide any documentation on requirements for configuring the zip file for a 3rd party Modbus device model compatible for upload to a PAS800.

 

According to the latest user guide for PAS800, Custom Models for Downstream Devices / Setting up the Parameters section, "Custom models are available on the EcoStruxure Panel Server webpages." However, PAS800 capability with 3rd party Modbus serial devices  appears to be limited to:

a. Offering end user an option to import a custom model by zip file (an empty folder is suggested) from the settings/Device models web page

b. Manually add unknown serial device type by slave ID from Settings/Modbus Discovery

c. Rename/Delete/update usage/name/virtual server/slave ID/observe connection status from Settings/Modbus devices

 

 

 

  • Thumbnail of EcoStruxure Panel Server Advanced
    Schneider Electric
    EcoStruxure Panel Server Advanced
View products (1)
Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-09-24 01:42 AM

0 Likes
9
4820
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-24 01:42 AM

Hi @swil , 

To answer your questions:

 

Q1. Does PAS800 support end users having the ability to create/use  custom device models?
No. For the moment, Custom Model creation is not integrated in the Panel Server web pages (unlike the Com'X).

 

Q2. Please provide any documentation on requirements for configuring the zip file for a 3rd party Modbus device model compatible for upload to a PAS800.

.zip file including your custom model is created through an external web portal (EcoStruxure Commissioning Web Portal). Only some experts can access this portal.


@Dom-Socquet or @Thierry_Baudard may give you more information regarding the custom model creation and roadmap of the feature.
@Guillaume_Evrard can also share some experience regarding the process.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 14
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-09-24 01:42 AM

0 Likes
9
4821
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-24 01:42 AM

Hi @swil , 

To answer your questions:

 

Q1. Does PAS800 support end users having the ability to create/use  custom device models?
No. For the moment, Custom Model creation is not integrated in the Panel Server web pages (unlike the Com'X).

 

Q2. Please provide any documentation on requirements for configuring the zip file for a 3rd party Modbus device model compatible for upload to a PAS800.

.zip file including your custom model is created through an external web portal (EcoStruxure Commissioning Web Portal). Only some experts can access this portal.


@Dom-Socquet or @Thierry_Baudard may give you more information regarding the custom model creation and roadmap of the feature.
@Guillaume_Evrard can also share some experience regarding the process.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
swil
Commander swil
Commander

Posted: ‎2022-09-24 01:49 PM . Last Modified: ‎2022-09-24 01:55 PM

1 Like
1
4809
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-24 01:49 PM

Thanks for the information @Romain_Polette,

 

PAS800 requirements for some projects, in order of importance, include:

1. Third party device creation (note we try hard to sell Schneider meters)

2. SFTP / FTP File push

3. A simple way of implementing 15 minute logging for selected parameters (if this is an issue - I'm unsure)

4. ETL solution for data backfill gateway data to PME database when comms problems arise

 

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-09-26 12:50 AM

1 Like
3
4770
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-26 12:50 AM

Hello,

 

As explained by Romain there is a cloud tool to build "custom model" called the Commissioning Web Portal. I do not know how it will be made available for all users. As of Today only the Global IoT Engineer for EAA are having access to it.

 

Pay attention that as of today we have some limitations with PAS/CWP. Only FC03 is available (Read Holding registers) and not all format are being supported.

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-09-26 12:51 AM

2 Likes
0
4769
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-26 12:51 AM

Hello,

 

SFTP should be in 1.5. As far as I have understood it should be the legacy Comx format....

Tags (1)
  • Tags:
  • english
Reply
swil
Commander swil
Commander

Posted: ‎2022-09-26 03:25 PM . Last Modified: ‎2022-09-26 03:31 PM

1 Like
1
4736
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-26 03:25 PM

Thanks Romain.

 

When does Schneider anticipate PAS800 firmware will be upgraded to to a level where it can be said that the PAS800 is suitable to replace Com'X 210/ Com'X 510?

Tags (1)
  • Tags:
  • english
Reply
swil
Commander swil
Commander

Posted: ‎2022-09-26 03:29 PM

0 Likes
2
4734
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-26 03:29 PM

Thanks for the information. For a current project read input registers is also required.

Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-09-26 11:28 PM

0 Likes
0
4717
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-26 11:28 PM

Hello swill,

 

There are many way to implement and install a com'X in a installation so I don't have a definitive and global answer to your question. However everybody must follow the roadmap and identify step by step when features are available.

 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-09-26 11:49 PM

0 Likes
1
4716
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-26 11:49 PM

 

I assume that you speak of the two native digital inputs of PAS800 when you mention "read input registers".

Tell me if my asumption is wrong and if it is something else.

 

Today, With the current fw1.4.0:

 

- it is possible to configure the two inputs as standard inputs or pulse conter in EPC (setting not available in web page)

- It is possible to collecte status and measurement in modbus registers

- it is not possible to view DI status and pulse counter value in measurement and trending of PAS800 web page

- it is not possible to publishDI status and pulse counter measure in the cloud for AA, RA,FE, EEH 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
swil
Commander swil
Commander

Posted: ‎2022-09-27 04:05 AM

0 Likes
0
4705
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-09-27 04:05 AM

I was referring to having ability to create third party devices that can read modbus input registers (registers numbered 3xxxx). 

 

Thanks for the information about pulse counters. We configured them in the PAS600L with EPC and that worked well.

Tags (1)
  • Tags:
  • english
Reply
geir_eas_no_bfo
Lt. Commander geir_eas_no_bfo
Lt. Commander

Posted: ‎2023-04-27 11:55 PM

0 Likes
1
3907
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-27 11:55 PM

Hi,

 

We are having problems with communication to third party devices via the PAS800L, We are using the PAS as a modbus gateway and read the devices from PLC.

Communication works good, but if we disconnect end device(ventilation fan) the PLC and PAS does not get com error, and communication does not start with return of power to the fan.

To establish connection again I have for reboot PAS.

What could be the reason for this?

Does PAS “buffer” modbus data for end devices? Thus, making PLC “think” that end device is still connected?

Might this be solved if end device was added as a custom model?

Then PAS will read data from modbus device and might be better at detecting loss of communication?

 

Must say that I`am suprised that Schneider doesn`t follow up with great functionality like in the old device ComX!

 

BR 

GIA

 

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-04-28 04:35 AM

0 Likes
0
3891
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-04-28 04:35 AM

Have you tried to upgrade to 1.5.1 ? 

If you want to use modbus tcp gateway, no device addition is expected. For sure you have internal data treatment but working as COMX.

If you configure the devices inside PAS, this should have no effect on the modbus trafic except to change the modbus id by the PAS virtual ID. However if you add a  "unknown device" you should get comm loss alarm on the PAS only. On the PLC side modbus shall detect comm loss by having no answer from device

Reply
sgirstl
sgirstl
Cadet

Posted: ‎2023-12-08 12:29 AM

0 Likes
0
3405
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-08 12:29 AM

Dear Romain,

We're highly interested in creating own custom models for PAS600.

Is there any update on that?

 

Best regards

 

Sebastian Girstl

noris network AG

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2023-12-08 08:19 AM

0 Likes
1
3379
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-08 08:19 AM

Hello @sgirstl , 

Some people in Germany have access to the Custom Model portal (EPC Web).

Better open a tech support ticket as usual. They will redirect you to the right people.

 

I can see you got an answer through case #105716738. 

 

For the moment, I do not know if EPC Web will be open to our partners.


Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Szymon_Hochół
Captain Szymon_Hochół Captain
Captain

Posted: ‎2023-12-11 03:57 AM

2 Likes
0
3321
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-12-11 03:57 AM

Hi @Romain_Polette , @sgirstl ,

The EPC Web portal should now be open for registration for Partners. Try: https://portal.cloud-commissioning.se.com/portal

 

BR

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore