PAS600L Modbus issue after replacing EGX100

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • PAS600L Modbus issue after replacing EGX100
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
106
Guillaume_Evrard
Commander Guillaume_Evrard Commander
49
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
31
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
smarques
Crewman smarques
Crewman

Posted: ‎2025-06-27 03:00 AM

0 Likes
11
279
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-27 03:00 AM

PAS600L Modbus issue after replacing EGX100

Good afternoon,

I had some EGX 100 gateway concentrators communicating with power analyzers via Modbus RTU and forwarding the data to the supervision system via Modbus TCP/IP.

 

However, some of the gateways failed due to age and were replaced with PAS600L units. Since the replacement, most of the analyzers are not communicating. They do communicate when I use a functional EGX 100, but not with the PAS600L. The configuration is the same on both.

 

I’ve noticed that the analyzers that do communicate are those with addresses higher than 10 or 12. This behavior is consistent across all three networks where the replacements were made, all showing the same results.

 

I appreciate your help.

Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
smarques
Crewman smarques
Crewman

Posted: ‎2025-07-04 02:52 AM

1 Like
1
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-04 02:52 AM

Hi.
Found the issue, for the TVR00210 to work the gateway needs to be configured with 2 stop bits (configuration with no parity bits), the CCM works with both 1 stop bit or 2 stop bits.
The EGX100 lacks the stop bit configuration.
The testing was done with a rather old software (PMC Modbus), is there any more recent version or a better software to do this?

Thanks @Guillaume_Evrard and @Romain_Polette for your time.

Best Regards.

See Answer In Context

Attachments
Reply
Replies 11
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-06-30 04:12 AM

1 Like
1
276
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-30 04:12 AM

Hello @smarques , 


PAS600L can be a transparent gateway for your devices. I do not expect any issue with basic Serial Modbus to Modbus TCP conversion.

 

EGX100 where also basic Ethernet Gateway. EGX300 was the former data concentrator (+ gateway).

 

Panel Server is very different with many feature regarding Cybersecurity. First things to check:

  1. What is your PAS600L FW ?
  2. did you enable Modbus TCP on Settings -> Network Communication -> Services ?
  3. How many analyser connected to each Panel Server ?
  4. Did you try to add the analyser to the PAS600L web interface ? Or are you using the PAS600 as a transparent gateway (no specific settings).
  5. Did you check PAS600 RS485 port settings (baudrate, parity) ?

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-06-30 09:05 PM

0 Likes
1
264
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-06-30 09:05 PM

hello @smarques 

As explained by Romain are you using the PAS600 as a transparent gateway (no configuration except serial modbus parameters) or as gateway with devices configured ? In that case PAS is replacing le modbus ID by the virtual ID. It might explain the issue with the ID >10 or 12 but normally PAS is keeping the ID for serial modbus.

Are you using 2Wires or 4 Wires ?

Kind Regards

Reply
smarques
Crewman smarques
Crewman

Posted: ‎2025-07-01 01:15 AM . Last Modified: ‎2025-07-02 01:39 AM

0 Likes
0
254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-01 01:15 AM

Hi,

  1. What is your PAS600L FW ? 001.006.000
  2. Did you enable Modbus TCP on Settings -> Network Communication -> Services ? Yes it is enabled, some of the analyzers are communicating with no problems, they are mostly the same model
  3. How many analyser connected to each Panel Server ? Around 15-20 per PAS600L
  4. Did you try to add the analyser to the PAS600L web interface ? Or are you using the PAS600 as a transparent gateway (no specific settings). I tried both methods, tried using it as a transparent gateway and adding the analyzer to the web interface, the results were the same, the analyzers that comunicated appeared as "connected" on the web interface.
  5. Did you check PAS600 RS485 port settings (baudrate, parity) ? Yes, as i mentioned above, some of the devices are communicating with no problems, some only communicate from time to time.

I also tried messing around with the modbus settings, like enabling the termination and polarizing resistors, messing with the times, etc, to no result.

Reply
smarques
Crewman smarques
Crewman

Posted: ‎2025-07-01 01:17 AM

0 Likes
0
254
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-01 01:17 AM

Hi, yes i have tried both, using it as a transparent gateway and with the devices configured, the result was the same, some devices fully communicate, some communicate from time to time, and some never communicate.

I am using a 2 wire configuration with shield.

Best regards.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-07-01 08:40 PM

0 Likes
3
248
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-01 08:40 PM

hello @smarques 

Are the devices connected identical ?

When added in the PAS config are you using a model or an unknwon device ?

Have you checked the modbus diag file to see the statistics when a device is configured ?

Kind Regards

Reply
smarques
Crewman smarques
Crewman

Posted: ‎2025-07-03 01:38 AM

0 Likes
2
219
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-03 01:38 AM

Hi, @Guillaume_Evrard,

I managed to get the schemes of one of the switchboards paired with the PAS600L, will try to get the rest soon, the ones that seem to not comunicate are micrologic 5.2E paired with the modbus module TVR00210.
The ones that comunicate are micrologic 5.0H and 5.0P paired with the CCM 33852 and ECO 48385.

I have tried to configure them using the model and as a unknown device, both with the same results, the logs report timeout.

Best Regards.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-07-03 09:10 PM

0 Likes
1
200
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-03 09:10 PM

hello @smarques 

OK got it I would say your issue is with 2W and 4W connections.

TRV00210 (legacy IFM) is providing 2W modbus, CCM for compact NS or Masterpact is providing 4 W modbus, pay attention that when using CCM you are getting multiple devices per Masterpact/Compact NS with slave ID that are automatically defined (PM, MM, BCM, CCM).

PAS supports only 2W.

 

 

Reply
smarques
Crewman smarques
Crewman

Posted: ‎2025-07-04 01:08 AM

0 Likes
0
171
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-04 01:08 AM

Hi @Guillaume_Evrard 
I will attach the schematic of the configuration, the CCM modules are then connected to a CJB306 with the toggle switch to 2W, to the PAS600L only 2 cables are connected + shield, the breakers with the CCM modules are the ones that i can read values fine, the ones that don´t work with the PAS600L but do work with the EGX100 are the ones paired with the TVR00210.
Again thanks for your time and your help it seems we are close to figure this out.
Best Regards.

Attachments
Reply
smarques
Crewman smarques
Crewman

Posted: ‎2025-07-04 02:52 AM

1 Like
1
172
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-04 02:52 AM

Hi.
Found the issue, for the TVR00210 to work the gateway needs to be configured with 2 stop bits (configuration with no parity bits), the CCM works with both 1 stop bit or 2 stop bits.
The EGX100 lacks the stop bit configuration.
The testing was done with a rather old software (PMC Modbus), is there any more recent version or a better software to do this?

Thanks @Guillaume_Evrard and @Romain_Polette for your time.

Best Regards.

Attachments
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2025-07-07 12:12 AM

1 Like
0
164
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-07 12:12 AM

Hi @smarques , 

Thanks for your feedback regarding TRV00210 and CCM configuration.

If you want to test communication with a Modbus device, Panel Server most recent firmware embed a Modbus testing web page.

Romain_Polette_0-1751872337596.png

 

You can try this as a first step to test Modbus communication (Serial or TCP) between Panel Server and Modbus device.

 

Regards, 

 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-07-07 04:59 AM . Last Modified: ‎2025-07-07 05:11 AM

1 Like
0
155
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-07-07 04:59 AM

image.pnghello @smarques ,

 

Thanks a lot, happy your issue is solved, it would mean that EGX100 is transparent in regards to the number of stop bits... which is not the case with PAS, good to know.   

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of