Gateways and Energy Servers
Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…
User | Count |
---|---|
82 | |
46 | |
29 | |
28 |
Link copied. Please paste this link to share this article on your social media post.
Hi,
I am currently simulating for a possible project, where several serial meters daisy chained to several PAS600 and at the end will be aggregated and logged by a PAS800L.
We have tried this using 2 PAS800L as per below scenario:
Child gateway has 4 serial meters iem3155 physically connected
Parent gateway - added the same 4 meters on the child gateway however they are dropping out and reconnecting then dropping out again.
Is there a setting we missed?
please see below screenshots. (Left is the child gateway, parent is on the right)
Thanks in advance,
Jiedan
Link copied. Please paste this link to share this article on your social media post.
hello @jedzruiz1985
Have you checked the modbus statistics on the parent and child gateway regarding timeout, exception codes ?
You have to tune the timeout connection on the parent PAS to allow the Child PAS to answer (modbus tcp settings) there is something in the manual.
Detection of communication is performed by the PAS every 15 s.
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Reading page 205 of DOCA0172EN-13 of the user guide. Can't understand it. lol. Is there a ways to show me how to do it?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Hello,
I would suggest x2 in the Parent = 4 vs 2 and 6 vs 3 ?
Have you checked the modbus statistics on both PAS ?
Kind Regards
Link copied. Please paste this link to share this article on your social media post.
Hi,
Can you elaborate what you mean when you say modbus statistics? Where to check it? is it this one please see screenshot
screenshot of the parent gateway
screenshot of child gateway
As I have read, I only need to change the message time outs right? or do I have to change modbus mode at the top as well?
Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.