Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Notifications
Login / Register
Community
Community
Notifications
close
  • Forums
  • Knowledge Center
  • Events & Webinars
  • Ideas
  • Blogs
Help
Help
  • Explore Community
  • Get Started
  • Ask the Community
  • How-To & Best Practices
  • Contact Support
Login / Register
Sustainability
Sustainability

We Value Your Feedback!
Could you please spare a few minutes to share your thoughts on Cloud Connected vs On-Premise Services. Your feedback can help us shape the future of services.
Learn more about the survey or Click here to Launch the survey
Schneider Electric Services Innovation Team!

MV SMD for PAS600

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • MV SMD for PAS600
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
99
Randi_Dolan
Commander Randi_Dolan Commander
46
Guillaume_Evrard
Commander Guillaume_Evrard Commander
44
Thierry_Baudard
Commander Thierry_Baudard Commander
30
View All
Related Products
product field
Schneider Electric
EcoStruxure Panel Server

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Solved
Alexander_Akulov
Crewman Alexander_Akulov Crewman
Crewman

Posted: ‎2024-06-06 02:59 AM . Last Modified: ‎2024-06-06 03:00 AM

0 Likes
12
2314
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-06 02:59 AM

MV SMD for PAS600

Hello Team,

 

In our project we met a problem with configuration of PAS600 for MV MCSet equipment. We couldn't find any software like LV SMD but for MV equipment. That's why it wasn't possible to create proper HMI view for MCSet. Does anyone know how to proceed in this case? Any thoughts or proposals are highly appreciated.

  • Thumbnail of EcoStruxure Panel Server
    Schneider Electric
    EcoStruxure Panel Server
View products (1)
Labels
  • Labels:
  • Commissioning
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-06-06 09:14 PM

1 Like
3
2259
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-06 09:14 PM

Hello @Alexander_Akulov 

 

For SMD LV or SMD MV you have to use the proper SMD configurator to generate the config file for the PLC and the Magellis if you have a Magellis.

For SMD LV PAS can be used as the zigbee gateway. For SMD MV today only ZBRN32 is supported. PAS Support should arrive soon (V7).

When you have a SMD MV you have to use :

SMD MV predefined model in the PAS (00_SMDxxxx), this model is coming with the ambient condition in the room and the Global alarm status ( None, Warning, Major).

For each of the function configured in the SMD (Cubicle, breaker) you have to import a custom model. Today there is a limitation in PAS as we are only able to configure one device with same modbus address ( serial or tcp). The workaround as the PLC is answering to all slave ID is to use a different ID for each function.

Example IP SMD = X

Substation X:1

Cubicle 1 X:2

Cubicle 2 X:3, etc

 

I can provide the custom models if you want, there are also the Active models used by the Factories

 

Kind Regards

See Answer In Context

Reply
Replies 12
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-06-06 05:30 AM

0 Likes
0
2290
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-06 05:30 AM

Hello, 

 

I do not think the MV SMD application is compatible with Panel Server. This application only use up to 3x ZBRN32 Zigbee Gateway. 

SMD Configurator tool for MV application exists, but is not compatible with Panel Server registers.

 

Romain_Polette_0-1717676455342.png

 

@claude.macri may help us on this topic.

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Alexander_Akulov
Crewman Alexander_Akulov Crewman
Crewman

Posted: ‎2024-06-06 07:00 AM

0 Likes
0
2287
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-06 07:00 AM

The problem is that we had LV Okken and MV MCSet in our project. LV plant has already installed PAS600 and customer wants to have identical equipment for LV and MV. We need to figure out somehow. Is there any way to connect HMI directly to PAS600, without PLC?   

Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2024-06-06 07:19 AM

0 Likes
0
2284
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-06 07:19 AM

Hi @Alexander_Akulov , 

Official HMI for Panel Server is the FDM128, but you can only view PowerTag data from Panel Server. FDM128 is not compatible with CL110 / TH110.

OKKEN team has validated Web HMI from Phoenix Contact. This Web HMI only display Panel Server Web interface. This HMI may not be qualified for MCSet application.

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-06-06 09:14 PM

1 Like
3
2260
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-06 09:14 PM

Hello @Alexander_Akulov 

 

For SMD LV or SMD MV you have to use the proper SMD configurator to generate the config file for the PLC and the Magellis if you have a Magellis.

For SMD LV PAS can be used as the zigbee gateway. For SMD MV today only ZBRN32 is supported. PAS Support should arrive soon (V7).

When you have a SMD MV you have to use :

SMD MV predefined model in the PAS (00_SMDxxxx), this model is coming with the ambient condition in the room and the Global alarm status ( None, Warning, Major).

For each of the function configured in the SMD (Cubicle, breaker) you have to import a custom model. Today there is a limitation in PAS as we are only able to configure one device with same modbus address ( serial or tcp). The workaround as the PLC is answering to all slave ID is to use a different ID for each function.

Example IP SMD = X

Substation X:1

Cubicle 1 X:2

Cubicle 2 X:3, etc

 

I can provide the custom models if you want, there are also the Active models used by the Factories

 

Kind Regards

Reply
Alexander_Akulov
Crewman Alexander_Akulov Crewman
Crewman

Posted: ‎2024-06-09 09:07 PM

0 Likes
2
2212
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-09 09:07 PM

Hello @Guillaume_Evrard,
In case I understood you correctly, we have two ways of solving this issue:
1) Official SMD MV with support of PAS. You said PAS support should arrive soon (V7). Could you please estimate when? Can we get something like Beta version of SMD MV with support of PAS?

2) Custom models. What are the next steps? What kind of information you need to get in order to provide proper custom model? 

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-06-09 09:11 PM

0 Likes
0
2209
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-06-09 09:11 PM

Hello @Alexander_Akulov 

 

1) this is only to replace ZBRN32 by PAS, no other change. I do not know when it will be released

2) Contact me directly providing number of cublicles and function of each cubicle as per SMD MV

Kind Regards 

Reply
Nikita
Nikita
Cadet

Posted: ‎2024-12-16 10:58 PM

0 Likes
4
1525
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-16 10:58 PM

Good afternoon, colleagues! I have a question: I need to add a TN110 sensor. There is a source configuration file, but there is no program through which I could add it. The user manual suggests the SMD configurator program (SMD MV). Can you tell me where I can download it?

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-12-17 08:38 PM

0 Likes
3
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-17 08:38 PM

Hello @Nikita ,

I guess you want to add TH110 but to what ?

Do you need SMD MV V7 configurator ? If yes what is your profile, are you a partner ?

Kind Regards

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2024-12-17 08:39 PM

0 Likes
0
1496
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-17 08:39 PM

@Alexander_Akulov FYI SMD MV V7 has been released.

Reply
Nikita
Nikita
Cadet

Posted: ‎2024-12-20 05:19 AM

0 Likes
2
1452
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-12-20 05:19 AM

The system consists of a ZBRN 32 zigbee concentrator, M251 PLC and an operator panel. Our profile is commissioning works, the company Di Group. We are your partner.

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-01-06 12:34 AM

0 Likes
0
1273
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-06 12:34 AM

Hello @Nikita ,

Have you been able to download SMD MV V7 ?

Kind Regards

Reply
Guillaume_Evrard
Commander Guillaume_Evrard Commander
Commander

Posted: ‎2025-01-07 09:21 PM

1 Like
0
1246
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2025-01-07 09:21 PM

Hello @Nikita ,

I got the info that today SMD MV configurator is not available for Partners, I would suggest to escalate your request to you SE representative.

Kind Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 
To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

This is a heading

With achievable small steps, users progress and continually feel satisfaction in task accomplishment.

Usetiful Onboarding Checklist remembers the progress of every user, allowing them to take bite-sized journeys and continue where they left.

of