Hi Everyone
We have a doubt about the Link150 gateway:
- We already read that the Link150 supports ION protocool with Firmware Link 150 Version 5.0.23 and thats great.
- Now we have a customer that wnats to integrate 4 SEPAM20 with its accesories ACE949-2 to modbus rtu.
- The customer also has an ION750 with only RS485.
- We wonder if we can integrate in only one Link150 gateway the ION 7500 meter and the 4 SEPAM20. the meter should be integrated to a new PME system with ION protocool and the Sepams with modbus. Is it posible? Or we have to use 2 Link150 gateways?. Attached an architecture.
Thanks in advance!!
Link copied. Please paste this link to share this article on your social media post.
Cannot, Link150 is ION or Modbus. It does not support both protocols at the same time.