Is there a way to pull diagnostics results from all EGX's in a system at the same time?
Link copied. Please paste this link to share this article on your social media post.
Hi Matt,
Currently I see 2 options for that:
1) See Dana Davidson post:
https://community.se.com/message/65969#65969
From each EGX300, after login, you may expect these pages under the root http://EGX_IP_Addr/:
General statistics page:
diagnostics.shtml
Active ModbusTCP/IP connections:
mbtcp_active.shtml
Remote ModbusTCP/IP and Serial devices statistics per device:
device_mbtcp_stats.shtml
Serial and Remote ModbusTCP/IP devices statistics per device (the same as above page, but in different order):
device_stats.shtml
HTTP accumulative connections (interesting for me):
http_past.shtml
HTTP active connections:
http_active.shtml
2) I believe that these pages are fed up with information that can be obtained via some Modbus Registers reads ... so to say using a ModbusTCP/IP Client connected to EGX300 ID:254 ...
You may have to contact R&D directly to get the registers list for that.
Regards,
Adrian