Is Smartlink A9XMSB11 firmware upgrade safe with EPC through Panel Server PAS600?

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Is Smartlink A9XMSB11 firmware upgrade safe with EPC through Panel Server PAS600?
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2022-11-09 05:45 AM

0 Likes
6
2132
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 05:45 AM

Is Smartlink A9XMSB11 firmware upgrade safe with EPC through Panel Server PAS600?

Can an upgrade of the Smartlink A9XMSB11 firmware be done with EcoStruxure Power Commission trough a Panel Server PAS600?

 

I tried it yesterday with two Smartlinks, and now they are not working anymore. The leds of both Smartlinks flashes green and red alternately. The Smartlinks had both very old firmware.

 

(Maybe it was also because the cable between the PC and the PAS600 was a bit damaged and there was sometimes loss of communication.)

Labels
  • Labels:
  • troubleshooting
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-11-16 08:06 AM

2 Likes
1
2032
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-16 08:06 AM

Hello,

 

It is possible to upgrade the firmware of a smartLink Modbus (A9XMSB11) through a panel server with the last version of  EPC-D 2.26.0 (test today with success with the default value of Modbus time out in Panel server -3 seconds)

Moreover, it is also possible to repair a broken SmartLink Modbus (after an unsuccessful upgrade firmware operation) through a Panel Server with the recovery mode:

In EPC :

  • Go in help>Discover and add devices>add via IP /ethernet> I cannot find Smartlink Modbus device after clicking on 'Find Devices'. What should I do?
  • Click on the button “MANUAL FIRMWARE UPGRADE” (screenshot1)
  • Fill the information in the parameter and click on ”start recovery button” to launch the operation (screenshot2)
  • When the recovery is ended, a message is displayed to inform user (screenshot 3)

 

  • screenshot1.jpgscreenshot2.jpgscreenshot3.jpg
Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 6
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-11-09 06:14 AM

1 Like
0
2122
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 06:14 AM

Hello,

 

No the reason is not your ethernet cable😊


Currently, the upgrade operation of the Smartlink A9XMSB11 with EPC through a Panel Server (PAS600 OR PAS800) are not supported and lead to the crash of the smartlink Modbus.

For the moment, the only way to recover the smartLink will be to remaster it with the old commissioning tool Smart test (More info on https://www.se.com/ww/en/faqs/FA414716/).

However to avoid the crash, we advise today to not follow the recommendation of upgrade proposed by EPC  and to not upgrade the smartLink modbus through a Panel Server !

 

A bug is also filled for the Panel Server R&D team and investigation are in progress. I will inform asap

Our apologize for this issue.

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-11-09 06:32 AM

1 Like
0
2121
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 06:32 AM

Hi @Philippe_Morel , 

 

For the moment, only upgrade through Smartlink SIB is recommended. This is mentioned in the SLMB user guide.

This is a known problem. Smartlink Modbus upgrade success through other gateway is random 😞

 

Regards, 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Philippe_Morel
Commander Philippe_Morel Commander
Commander

Posted: ‎2022-11-16 02:37 AM

0 Likes
3
2048
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-16 02:37 AM

I could repair both Smartlink by using Smart Test. It did not work with an EGX as gateway, it only did when using a direct connection (COM). I had no Smartlink Ethernet as gateway. A 'repair' button appears after waiting a very long time in the software Smart Test. The first time I tried the repair button I got an error message, but when I launched it directly after for a second time it does repair the Smarlink. This was the case for both Smarlink.

Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-11-16 04:39 AM

0 Likes
2
2040
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-16 04:39 AM

Hi @Philippe_Morel , 

The repair process with Smart Test can be random sometimes... but always worked for me.

You can also experienced some upgrade failure with direct COM connection. There are some known issue with this process.

 

Regards,     

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-11-16 08:06 AM

2 Likes
1
2033
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-16 08:06 AM

Hello,

 

It is possible to upgrade the firmware of a smartLink Modbus (A9XMSB11) through a panel server with the last version of  EPC-D 2.26.0 (test today with success with the default value of Modbus time out in Panel server -3 seconds)

Moreover, it is also possible to repair a broken SmartLink Modbus (after an unsuccessful upgrade firmware operation) through a Panel Server with the recovery mode:

In EPC :

  • Go in help>Discover and add devices>add via IP /ethernet> I cannot find Smartlink Modbus device after clicking on 'Find Devices'. What should I do?
  • Click on the button “MANUAL FIRMWARE UPGRADE” (screenshot1)
  • Fill the information in the parameter and click on ”start recovery button” to launch the operation (screenshot2)
  • When the recovery is ended, a message is displayed to inform user (screenshot 3)

 

  • screenshot1.jpgscreenshot2.jpgscreenshot3.jpg
Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-11-16 11:08 PM

0 Likes
0
2016
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-16 11:08 PM

That is great news @Thierry_Baudard !

Thanks for sharing.

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore