How to connect third-party Modbus devices to panel server

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • How to connect third-party Modbus devices to panel server
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Related Products
product field
Schneider Electric
EcoStruxure Panel Server Universal

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Stuart_Cheng
Lt. Commander Stuart_Cheng Lt. Commander
Lt. Commander

Posted: ‎2022-11-21 08:03 AM

0 Likes
9
5210
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-21 08:03 AM

How to connect third-party Modbus devices to panel server

Hi All,

 

From the official presentation, we know that a panel server can also be used to collect data from third-party devices. However, I could not find any detailed procedure on how to connect and map the registers. Does anyone have relevant information? Thank you

  • Thumbnail of EcoStruxure Panel Server Universal
    Schneider Electric
    EcoStruxure Panel Server Universal
View products (1)
Labels
  • Labels:
  • Commissioning
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-11-21 08:12 AM

0 Likes
7
5203
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-21 08:12 AM

Hello,

 

There is a cloud based tool called Commisioning Web portal to create "models" to be loaded on the PAS using the Web Pages.

As of today only few SE Employees are having access to the tool.

Pay attention that some limitations exist with FW 1.4 and 1.5 regarding modbus communication ( Only FC03 read holding register, same endianess for all the measurements, ....)

 

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 9
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-11-21 08:12 AM

0 Likes
7
5204
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-21 08:12 AM

Hello,

 

There is a cloud based tool called Commisioning Web portal to create "models" to be loaded on the PAS using the Web Pages.

As of today only few SE Employees are having access to the tool.

Pay attention that some limitations exist with FW 1.4 and 1.5 regarding modbus communication ( Only FC03 read holding register, same endianess for all the measurements, ....)

 

 

Tags (1)
  • Tags:
  • english
Reply
Eric_HAVAS
Lt. Commander Eric_HAVAS Lt. Commander
Lt. Commander

Posted: ‎2022-11-22 12:16 AM

0 Likes
4
5168
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-22 12:16 AM

Hello Stuart,

 

I remind that  you are one of this only few SE Employees who have already access to this web portal (CWP) to create custom models for their countries.
Regards

Eric

Tags (1)
  • Tags:
  • english
Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2022-11-25 01:37 AM

2 Likes
3
5091
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-25 01:37 AM

Hello,

I also to add one comment about Custom model in Panel Server.

If the need is just to collect Modbus registers from downstream products in a Modbus TCP/IP client through the Panel Server (example PME used with modbus drivers for connected products), Custom models are not needed.In this case, The Panel Server just acts as a Transparent gateway (such as Link150) and will forward the Traffic (even if the product are not discovered in the Panel Server)

Custom model for Downstream product will be mandatory only if the Panel Server is used as A Local energy Server or for Schneider Electric Cloud connection,

 

For my two cents !

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-11-25 01:56 AM

0 Likes
2
5086
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-25 01:56 AM

and do not configure the devices in PAS to not replace the modbus ID by the virtual ID....

Tags (1)
  • Tags:
  • english
Reply
PerFrederiksen
PerFrederiksen Cadet
Cadet

Posted: ‎2023-02-14 01:54 PM

0 Likes
1
4687
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-14 01:54 PM

"and do not configure the devices in PAS to not replace the modbus ID by the virtual ID...."

So virtual ID should not be enabled if the panel server is used to just read  holding registers from various devices ?

BR Per

 

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2023-02-14 10:03 PM

0 Likes
0
4672
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-14 10:03 PM

PAS and COMX are working in the same way regarding modbus gateway.

If there is a virtual ID matching the ID requested by the poller it will be "forwarde" to the device. If there is no Virtual ID matching, the frames should be pushed to the serial interface for the device with ID = ID requested.

Reply
Thierry_Baudard
Commander Thierry_Baudard Commander
Commander

Posted: ‎2023-02-14 11:13 PM

0 Likes
0
4663
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2023-02-14 11:13 PM

Hello,

 

A video previously posted to illustrate what are a Modbus ID and a Modbus Virtual Server ID

Panel Server Video è Server ID and virtual Server ID 

Thierry BAUDARD
EcoStruxure Power- Technical Support Expert for Softwares & Solutions
Reply
Christopher.odonnell
Lieutenant | EcoXpert Master Christopher.odonnell Lieutenant | EcoXpert Master
Lieutenant | EcoXpert Master

Posted: ‎2024-05-27 01:26 AM

0 Likes
1
3007
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-27 01:26 AM

Trying to add an Exertherm data card to a PAS600L but cannot manually add any help on how to do so would be great.

 

Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2024-05-27 08:50 PM

0 Likes
0
2988
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2024-05-27 08:50 PM

Hello @Christopher.odonnell,

Are you facing issue to create the model with EPC W or adding the device in PAS ?

I guess that you want to collect data from the thermal monitoring and not use the PAS as a modbus tcp gateway ?

Kind Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.