Gmail configuration for Com'X 210 / Com'X510

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Gmail configuration for Com'X 210 / Com'X510
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
Thierry_Baudard
Commander Thierry_Baudard Commander
32
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
sesa74337_bridg
Lt. Commander sesa74337_bridg Lt. Commander
Lt. Commander

Posted: ‎2017-05-08 11:02 PM

2 Likes
8
1857
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-08 11:02 PM

Gmail configuration for Com'X 210 / Com'X510

Hi, All,

I would like to know if there is an application notes on how to configure the Email (SMTP) function for Com'X (210 or 510). Customer would like to use Gmail SMTP Server , is that possible? What is the minimum firmware version? Thank you for your help

Regards,

James

Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2017-05-11 01:33 AM

0 Likes
1
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-11 01:33 AM

Jun 'James' Rong​
Hi

Yes today  Com'X doesn't support any SMTP with  encryption/transport  layer SSL/TLS security , in the next release this will be possible ,   but you can use google unencrypted restricted Gmail SMTP server aspmx.l.google.com, Port 25

(Per user receiving limits apply. This option restricts sending messages to Gmail or G Suite users only, mail can only be sent to Gmail or G Suite users, TLS not required......)

Use SMTP settings to send mail from a printer, scanner, or app - G Suite Administrator Help

On com'x user guide  you will find how to configure a publication/ cvs export using  SMTP protocol

1. Click Settings > General Settings > Publication.

2. Select CSV export in the Destination platform drop-down list.

3. Select SMTP in the Protocol drop-down list.

4. Type the address of the server transporting the data in the Server field    aspmx.l.google.com

5. Type the outgoing delivery port in the Port field. select 25.

6. Select No in the Authentication required field

7. Save changes

Screenshot - 5_11_2017 , 10_25_40 AM.jpg

See Answer In Context

Reply
Replies 8
Abdel
Lieutenant Abdel Lieutenant
Lieutenant

Posted: ‎2017-05-10 12:45 PM

0 Likes
0
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-10 12:45 PM

The Com'x platform doesn't support SMTP with SSL or TLS. Hence gmail will not work

Reply
Abdel
Lieutenant Abdel Lieutenant
Lieutenant

Posted: ‎2017-05-10 01:41 PM

1 Like
0
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-10 01:41 PM

I'v just read that in the next release (q2 this year) the encryption will be supported 

Reply
Anonymous user
Not applicable

Posted: ‎2017-05-11 01:33 AM

0 Likes
1
1708
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-05-11 01:33 AM

Jun 'James' Rong​
Hi

Yes today  Com'X doesn't support any SMTP with  encryption/transport  layer SSL/TLS security , in the next release this will be possible ,   but you can use google unencrypted restricted Gmail SMTP server aspmx.l.google.com, Port 25

(Per user receiving limits apply. This option restricts sending messages to Gmail or G Suite users only, mail can only be sent to Gmail or G Suite users, TLS not required......)

Use SMTP settings to send mail from a printer, scanner, or app - G Suite Administrator Help

On com'x user guide  you will find how to configure a publication/ cvs export using  SMTP protocol

1. Click Settings > General Settings > Publication.

2. Select CSV export in the Destination platform drop-down list.

3. Select SMTP in the Protocol drop-down list.

4. Type the address of the server transporting the data in the Server field    aspmx.l.google.com

5. Type the outgoing delivery port in the Port field. select 25.

6. Select No in the Authentication required field

7. Save changes

Screenshot - 5_11_2017 , 10_25_40 AM.jpg

Reply
Anonymous user
Not applicable

Posted: ‎2017-08-08 06:06 PM

0 Likes
0
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2017-08-08 06:06 PM

Thanks Lazaro

I have configured my ComX'200 using the SMTP gmail server and my personal e-mail (publication is Ok)

But I can't see it in my imbox

Thanks in advance for your comments

Bryan

Reply
sesa249965_brid
Ensign sesa249965_brid Ensign
Ensign

Posted: ‎2018-02-19 07:46 AM

1 Like
3
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-19 07:46 AM

Hi All,

I would like to share the tutorial I prepared to configure Gmail using the new Com'X510 firmware (v.4.0.10).

As you know the Com'X510 v.4.0.10 support SMTP, so now it's possible to use the smtp.gmail server.

https://schneider-electric.box.com/v/ComX510-GmailSMTP-Andean

I hope it would be helpful !!

Best regards,

William,

Reply
Anonymous user
Not applicable

Posted: ‎2018-02-26 07:56 PM

1 Like
0
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-26 07:56 PM

Hi William

Thank you for sharing. In the absence Gmail server I had to use SMTP2GO but now is good to know that we can use Gmail.

Regards

Bryan C.

Reply
Anonymous user
Not applicable

Posted: ‎2018-02-27 11:41 AM

0 Likes
1
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-27 11:41 AM

Hey William,

This guide is extremely helpful! Do you mind if we share this?

Best,

Colton

Reply
sesa249965_brid
Ensign sesa249965_brid Ensign
Ensign

Posted: ‎2018-02-27 02:18 PM

0 Likes
0
1707
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2018-02-27 02:18 PM

Hi Colton,

Not at all, that was my main purpose when I did the tutorial, so feel free to share it,

Regards,

William

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support
Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore