FDM128 not displaying correct information from IFE unit connected to Micrologics

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • FDM128 not displaying correct information from IFE unit connected to Micrologics
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Back to Gateways and Energy Servers
Start a Topic
Anonymous user
Not applicable

Posted: ‎2020-03-13 01:29 AM

0 Likes
2
1165
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-13 01:29 AM

FDM128 not displaying correct information from IFE unit connected to Micrologics

Good Day, I require some assistance with this unusual problem:

 

I have four LVD Boards each with its own FDM128 HMI unit. 

Each of these units connects to a minimum of 4 IFE units and a maximum of 8.

Each of the IFE units are connected to a Micrologic 5.0 E unit.

 

The FDM128 has an Editor version : 6.2.3:5072 and a Runtime Version :6.2.3.5074

 

The below information I retrieved while online on the IFE Web Page.

The IFE has a Version: 3.7.24

The BCM ULP has a Version: V4.1.9

 

What happens is, only two of the four FDM128 units indicates that some of the IFE/Micrologic units show incorrect data the rest indicate correctly. Attached is two photos. When the breaker is in the open status the FDM indicates "Trip SDE", when it is in the closed status the FDM unit indicates "NA".

 

I have a separate PME and PSO system communicating directly to these units as well and when I look on Vista it indicates the correct status.

 

Any advise what the problem could be?

 

Regards

 

 

 

Attachments
Reply
  • All forum topics
  • Previous Topic
  • Next Topic
Replies 2
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2020-03-13 04:35 AM

0 Likes
1
1162
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-13 04:35 AM

Hello @Anonymous user 

We do not support LV434128 in this Community.

 

Do you know if your 4 FDM128 have the same application version ?

 

If PME and PSO can poll data from your IFE, your issue may be related to the FW version of your FDM128 that is quite old....

And I do not see that 6.2.3 is an official version in the Release Notes : https://download.schneider-electric.com/files?p_enDocType=Software+-+Release+Notes&p_File_Name=DOCA0151EN-02.pdf&p_Doc_Ref=DOCA0151EN

 

Can you try to upgrade your FDM128 Application with the latest version ?

https://download.schneider-electric.com/files?p_enDocType=Firmware+-+Updates&p_File_Name=EnerlinX_FDM128_firmware_V8_0_12.zip&p_Doc_Ref=EnerlinX_FDM128_software

 

Regards.

 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • FDM128
Reply
Anonymous user
Not applicable

Posted: ‎2020-03-16 12:59 AM

0 Likes
0
1159
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2020-03-16 12:59 AM

Thank you for your response.

 

I will give this a try.

 

Regards

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore