FDM128 HMI showing values from CL110
Hi!
Is it possible to connecting FDM128 HMI trough Panel Server Universal to a CL110 Enviroment sensor
I have the set up where i have 6 CL110 connected to my Panel Server and want to show then on EG. FDM128 HMI. but cant find any supported device list for this HMI
Regards. Nikolaj Johansen
El-Tek Automation ApS EcoXpert Partner: Certified Critical Power
Link copied. Please paste this link to share this article on your social media post.
2024-12-2012:59 AM
Hello @niko556a You can refer to FDM128 user guide, chapter "Monitored Devices Through EcoStruxure Panel Server Gateway" to get the list of products that you can address through the panel server: https://www.se.com/fr/fr/download/document/DOCA0037EN/ Regards