Energy reading showing Zero value
Hello PME team,
I am using EGX 300 , I am trying to monitoring the Energy value of EM 6400 on EGX 300.
But it showing zero value, I have attached snaps of the error.
Kindly suggest me to fix the issue.
Regards,
Abbyshek
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Moved to the gateways Area.
Juan
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Hi Abhishak,
Is there any energy values are accumulated in the EM6400 meter? Since only the voltage & frequency is displayed. Apply some load current and check, is the power and energy values are updating.
If the values are still not updating, please read and share the registers values starting from 3957 (8 registers).
Posted: 2017-04-11 10:38 PM
- Mark as New
- Bookmark
- Subscribe
- Mute
- Subscribe to RSS Feed
- Permalink
- Email to a Friend
- Report Inappropriate Content
Link copied. Please paste this link to share this article on your social media post.
Thanks for quick reply,
I will try to apply some load on it , check it while its updating or not.