EGX150 Modbus Gateway- Maximum Supported Distance for Belden 9841 Cable

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • EGX150 Modbus Gateway- Maximum Supported Distance for Belden 9841 Cable
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
116
Guillaume_Evrard
Captain Guillaume_Evrard Captain
58
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
shemil_usman
Ensign shemil_usman
Ensign

Posted: ‎2022-11-09 12:33 PM

0 Likes
2
1760
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 12:33 PM

EGX150 Modbus Gateway- Maximum Supported Distance for Belden 9841 Cable

Hi,

 

We have 3 generators to the looped and connected via Modbus port using Belden 9841 cable to EGX150 gateway.

 

The generators are far away from the Data Center at a distance of 600 meters.

 

The EGX150 will be installed in the Data Center rack and so please advise if this distance is supported, and that all parameters will be available without any disruption.

 

Thanks & Regards

Shemil

Labels
  • Labels:
  • Legacy Gateways & Energy Servers
Tags (1)
  • Tags:
  • english
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-11-09 11:06 PM

0 Likes
0
1747
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 11:06 PM

Hi @shemil_usman , 

 

Link150 is not different than any other Modbus device.

 

You must respect some cabling rules / best practices:

https://electrical-engineering-portal.com/correct-cabling-modbus-rs485

https://www.se.com/ww/en/faqs/FA221785/

 

If you follow the wiring rules above, installing the Link150 600m far away from the Modbus Slaves (generators) should work fine.

regards, 

Romain POLETTE
Solution Architect - France Operations

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-11-09 11:50 PM

0 Likes
0
1742
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 11:50 PM

Hello,

depending on the size of the belden cable you can reach up to 1300m at 19200bps . Do not forget EOL resistance 

Pay attention to the Eart/ ground network as the cable is shielded, if you span over different grids you can face issues.

 

COMX wiring guide : DOCA0035EN is providing very good information on modbus wiring 

 

9841 (1 pair) is the Belden approved cable for modbus communication.

 

See Answer In Context

Tags (1)
  • Tags:
  • english
Reply
Replies 2
Romain_Polette
Kirk Romain_Polette Kirk
Kirk

Posted: ‎2022-11-09 11:06 PM

0 Likes
0
1748
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 11:06 PM

Hi @shemil_usman , 

 

Link150 is not different than any other Modbus device.

 

You must respect some cabling rules / best practices:

https://electrical-engineering-portal.com/correct-cabling-modbus-rs485

https://www.se.com/ww/en/faqs/FA221785/

 

If you follow the wiring rules above, installing the Link150 600m far away from the Modbus Slaves (generators) should work fine.

regards, 

Romain POLETTE
Solution Architect - France Operations
Tags (1)
  • Tags:
  • english
Reply
Guillaume_Evrard
Captain Guillaume_Evrard Captain
Captain

Posted: ‎2022-11-09 11:50 PM

0 Likes
0
1743
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2022-11-09 11:50 PM

Hello,

depending on the size of the belden cable you can reach up to 1300m at 19200bps . Do not forget EOL resistance 

Pay attention to the Eart/ ground network as the cable is shielded, if you span over different grids you can face issues.

 

COMX wiring guide : DOCA0035EN is providing very good information on modbus wiring 

 

9841 (1 pair) is the Belden approved cable for modbus communication.

 

Tags (1)
  • Tags:
  • english
Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore