EBX 200 doesn't have serial device PM5331 in its table for devices

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • EBX 200 doesn't have serial device PM5331 in its table for devices
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
Zelislav
Ensign Zelislav Ensign
Ensign

Posted: ‎2014-05-18 10:06 PM

0 Likes
2
839
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-05-18 10:06 PM

EBX 200 doesn't have serial device PM5331 in its table for devices

Halo everybody,


In our country we have new law where we need for metering couple new things. I need to have device with MID certificate. PM5111, PM5331, PM5341 and PM5561 are have it. That is ok, but... In EBX 200 list for creating new device, PM5331 doesn't exist. There is PM5111 and PM5561 but another PM5331 and PM5341 are not there.
I need ASAP information about this device PM5331. Could I use PM5330 instead PM5331 from list of EBX200?

It is very important. I have project where I need to know this.

Do anybody know, in the future will be in EBX posibility create a device type PM5331?

Thank you.

Tags (2)
  • Tags:
  • com'x200
  • firmware
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
Anonymous user
Not applicable

Posted: ‎2014-05-19 08:40 AM

0 Likes
0
805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-05-19 08:40 AM

I confirm, PM5330 has been introduce to late in order to include it into the version, 1.1.15.

(it was too late to provision this device for the verification tests)

It has been added in the future release

(it is already included in the intermediate private version)

Before this next public version,

The autodiscovery will not discover your PM5331 and you must declare it as a PM5330 (the modbus interface is the same)

     Regards

     Jef

See Answer In Context

Reply
Replies 2
sesa126586
sesa126586 Schneider Alumni (Retired)
Schneider Alumni (Retired)

Posted: ‎2014-05-19 06:55 AM

0 Likes
1
805
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-05-19 06:55 AM

Hi Zelislav,

Please use PM5330 instead. The last digit (1) in case of MID references is just for the MID compliance and the register point map should not change. Using PM5330 should work.

Best,

Neel

Reply
Anonymous user
Not applicable

Posted: ‎2014-05-19 08:40 AM

0 Likes
0
806
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-05-19 08:40 AM

I confirm, PM5330 has been introduce to late in order to include it into the version, 1.1.15.

(it was too late to provision this device for the verification tests)

It has been added in the future release

(it is already included in the intermediate private version)

Before this next public version,

The autodiscovery will not discover your PM5331 and you must declare it as a PM5330 (the modbus interface is the same)

     Regards

     Jef

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore