Halo everybody,
In our country we have new law where we need for metering couple new things. I need to have device with MID certificate. PM5111, PM5331, PM5341 and PM5561 are have it. That is ok, but... In EBX 200 list for creating new device, PM5331 doesn't exist. There is PM5111 and PM5561 but another PM5331 and PM5341 are not there.
I need ASAP information about this device PM5331. Could I use PM5330 instead PM5331 from list of EBX200?
It is very important. I have project where I need to know this.
Do anybody know, in the future will be in EBX posibility create a device type PM5331?
Thank you.
Posted: 2014-05-19 08:40 AM
Link copied. Please paste this link to share this article on your social media post.
I confirm, PM5330 has been introduce to late in order to include it into the version, 1.1.15.
(it was too late to provision this device for the verification tests)
It has been added in the future release
(it is already included in the intermediate private version)
Before this next public version,
The autodiscovery will not discover your PM5331 and you must declare it as a PM5330 (the modbus interface is the same)
Regards
Jef
Link copied. Please paste this link to share this article on your social media post.
Hi Zelislav,
Please use PM5330 instead. The last digit (1) in case of MID references is just for the MID compliance and the register point map should not change. Using PM5330 should work.
Best,
Neel
Posted: 2014-05-19 08:40 AM
Link copied. Please paste this link to share this article on your social media post.
I confirm, PM5330 has been introduce to late in order to include it into the version, 1.1.15.
(it was too late to provision this device for the verification tests)
It has been added in the future release
(it is already included in the intermediate private version)
Before this next public version,
The autodiscovery will not discover your PM5331 and you must declare it as a PM5330 (the modbus interface is the same)
Regards
Jef