Datalog files are sent in Chinese instead of English

Gateways and Energy Servers

Schneider Electric support forum to share knowledge about product selection, installation and troubleshooting for EcoStruxure Panel Server, PowerTag, Com'X, Link150…

Search in

Improve your search experience:

  • Exact phrase → Use quotes " " (e.g., "error 404")
  • Wildcard → Use * for partial words (e.g., build*, *tion)
  • AND / OR → Combine keywords (e.g., login AND error, login OR sign‑in)
  • Keep it short → Use 2–3 relevant words , not full sentences
  • Filters → Narrow results by section (Knowledge Base, Users, Products)
cancel
Turn on suggestions
Auto-suggest helps you quickly narrow down your search results by suggesting possible matches as you type.
Showing results for 
Show  only  | Search instead for 
Did you mean: 
  • Home
  • Schneider Electric Community
  • EcoStruxure Power & Grid
  • Gateways and Energy Servers
  • Datalog files are sent in Chinese instead of English
Options
  • Mark Topic as New
  • Mark Topic as Read
  • Float this Topic for Current User
  • Bookmark
  • Subscribe
  • Mute
  • Printer Friendly Page
Invite a Co-worker
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send Invite Cancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Send New Invite Close
Top Experts
User Count
Romain_Polette
Kirk Romain_Polette Kirk
117
Guillaume_Evrard
Captain Guillaume_Evrard Captain
59
Randi_Dolan
Commander Randi_Dolan Commander
46
View All

Recommended Forums

  • Metering & Power Quality

  • SmartConnector Forum

Invite a Colleague

Found this content useful? Share it with a Colleague!

Invite a Colleague Invite
Solved Go to Solution
Back to Gateways and Energy Servers
Start a Topic
Solved
QuanGUO
Lieutenant QuanGUO Lieutenant
Lieutenant

Posted: ‎2014-07-28 08:09 AM

0 Likes
3
1152
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-28 08:09 AM

Datalog files are sent in Chinese instead of English

Team,

We have notified a weird issue in one of our REM EGX300. The Datalog files are sent in Chinese instead of English.

网关名称;网关序列号;网关IP地址;网关MAC地址;设备名称;设备本地 ID;设备类型ID;设备类型名称;记录间隔;历史间隔次数

EGX300;53109731;10.140.164.17;00:80:67:86:52:BE;CN-HZ1-M-25W-01;1;32500;PM3250/PM3255;15;0

;;;主题ID1;主题ID2;主题ID3;主题ID4;主题ID5

;;;1617;1621;1625;1731;1008

错误;时区(UTC偏移) (分钟);本地时间戳;视在电能 (kVAh);有功电能(kWh);无功电能(kVARh);需量有功 (kW);相电流平均值

0;480;2014-07-28 15:15:00;416311,690;411154,974;58915,331;222,820;350,485

0;480;2014-07-28 15:30:00;416368,144;411210,851;58923,379;223,480;354,485

0;480;2014-07-28 15:45:00;416423,598;411265,719;58931,424;219,495;336,480

0;480;2014-07-28 16:00:00;416477,742;411319,272;58939,394;214,210;328,482

I guess someone unaware changed a special setting in EGX300. Unfortunately I don't know how to recover the description setting in English. Who can do me a favor?

Many thanks in anticipation!

Best regards,

Quan

Tags (2)
  • Tags:
  • datalog
  • language
Reply
  • All forum topics
  • Previous Topic
  • Next Topic

Accepted Solutions
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-07-28 09:19 AM

0 Likes
1
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-28 09:19 AM

Hello Quan,

Log into your EGX300 as an Administrator and change the language setting to English:

1. Click on Setup

2. Click User Accounts

3. Change the Language for the Administrator user account

See images below:

4237

4238

I hope this helps.

James

See Answer In Context

Reply
Replies 3
JamesJeanette
Commander JamesJeanette Commander
Commander

Posted: ‎2014-07-28 09:19 AM

0 Likes
1
1115
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-28 09:19 AM

Hello Quan,

Log into your EGX300 as an Administrator and change the language setting to English:

1. Click on Setup

2. Click User Accounts

3. Change the Language for the Administrator user account

See images below:

4237

4238

I hope this helps.

James

Reply
QuanGUO
Lieutenant QuanGUO Lieutenant
Lieutenant

Posted: ‎2014-07-28 06:16 PM

0 Likes
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-07-28 06:16 PM

Hello James,

Thanks for your answer! It means that Datalog should be recorded into files with Admininistrator Language setting. Also I need to create a specific account which will be used by local maintance engineers. The admininstrator account might be hidden.

Thanks again.

Quan

Reply
LaurentCoene
Captain LaurentCoene Captain
Captain

Posted: ‎2014-08-01 02:23 AM

1 Like
0
1114
  • Mark as New
  • Bookmark
  • Subscribe
  • Mute
  • Permalink
  • Print
  • Email to a Friend
  • Report Inappropriate Content

Link copied. Please paste this link to share this article on your social media post.

‎2014-08-01 02:23 AM

Actually, there's an easier way that will avoid you to have to create different accounts. There's an hidden page that will allow you to set the export language to English. Just go to HTTP://<IP_Address>/evo_compatibility.shtml

4270

Just check the box "Always Export in English".

Boom, you're done! 🙂

Reply
Preview Exit Preview

never-displayed

You must be signed in to add attachments

never-displayed

 

You’ve reached the end of your document

WHAT’S NEXT?

Ask our Experts

Didn't find what you are looking for? Ask our experts!

My Dashboard

Check out the new Feeds and activities that are relevant to you.

To The Top!

Forums

  • APC UPS Data Center Backup Solutions
  • EcoStruxure IT
  • EcoStruxure Geo SCADA Expert
  • Metering & Power Quality
  • Schneider Electric Wiser

Knowledge Center

Events & webinars

Ideas

Blogs

Get Started

  • Ask the Community
  • Community Guidelines
  • Community User Guide
  • How-To & Best Practice
  • Experts Leaderboard
  • Contact Support

    Ask our Experts

    Have a question related to our products, solutions or services? Get quick support on community Forums

    Email Us

    For Community platform-related support, please email us

Brand-Logo
Subscribing is a smart move!
You can subscribe to this board after you log in or create your free account.
Forum-Icon

Create your free account or log in to subscribe to the board - and gain access to more than 10,000+ support articles along with insights from experts and peers.

Register today for FREE

Register Now

Already have an account? Login

Terms & Conditions Privacy Notice Change your Cookie Settings © 2025 Schneider Electric

Welcome!

Welcome to your new personalized space.

of

Explore